rv4jimnme
Explorer
Explorer
Noticed that Generator runs the A/C but if I turn off the A/C then turn it back on the Generator will shut down. I can restart the Generator and then turn on a/C and it will work. Just wondering why?
Fleetwood Tioga 2011 Mercedes Chassis 24L one a/c.
5 REPLIES 5

rv4jimnme
Explorer
Explorer
THANKS SO MUCH! Waited 5 minutes and it worked!
Marlene

CA_Traveler
Explorer III
Explorer III
My rig has automatic delays - first in the ATS and then the A/Cs.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

2oldman
Explorer
Explorer
rv4jimnme wrote:
... if I turn off the A/C then turn it back on the Generator will shut down..
Why do you do that?
"If I'm wearing long pants, I'm too far north" - 2oldman

Jack_Diane_Free
Explorer
Explorer
Totally agree with DrewE. Just wait a few minutes before turning A/C back on. The genny is overloading trying to start against the pressure in the A/C.

DrewE
Explorer
Explorer
How long are you waiting between turning the AC off and then on? If you don't let it sit for a couple minutes for the pressure in the system to equalize, it's trying to start the compressor against a pressure head and that's a significant extra load (both for the generator and the compressor motor).

Many thermostats have a time delay to prevent restarting the AC right after it's been turned off, for this very reason. Many others lack that nicety.