When I ran a 100 ft drop cord out to motor home to keep ref working the tranfer switch keeps clicking on an off
21 REPLIES 21

tropical36
Explorer
Explorer
hohenwald48 wrote:
I think the progressive low voltage drop out is set to 104 volts. If that's a cheapo 16 gauge extension cord. You will have about 13-15 percent voltage drop so you would need at least 120 volts coming in to the cord to keep the voltage at the distant end above the Progressive drop out voltage level.

I suspect your problem has no relationship to the transfer switch but power disconnect is occurring due to the Progressive detecting a low voltage condition. The Progressive contactor is the thunk you're hearing and not the transfer switch.

I think you probably need a shorter and/or fatter cord.

That makes better sense, if the OP should have one of those low voltage sensors.
I've learned some, since posting, cuz I had some problems of my own, upon arriving at our location on Thursday afternoon.
Story short, I was missing the neutral return, with shore power and I think because the twist loc shore cord wasn't seating and tightened properly. Took care of some other things along the way to this probable discovery, including some wiring heat damage inside the transfer switch, due to loose connections. What I found out with it's operation, is that shore power goes straight through the normally closed contacts, so not much to normally prevent it from low voltage there. The genset uses the NO contacts and as a result takes priority over the power feed, so when it starts, it first delays, utilizing a PC board inside and then the contacts close for energizing the circuit box, regardless of power from the shore or not. It's possible that the genset wouldn't transfer with low voltage, I guess.
Anyway and unless you have other sophisticated equipment inline, there's not much to prevent low voltage from shore power and I've seen plenty of it, in our travels.
"We are often so caught up in our destination that we forget to appreciate the journey."

07 Revolution LE 40E_Spartan MM_06 400HP C9 CAT_Allison 3000.

Dinghy_2010 Jeep Wrangler JKU ISLANDER.

1998 36ft. National Tropi-Cal Chevy Model 6350 (Sold)

hohenwald48
Explorer
Explorer
I think the progressive low voltage drop out is set to 104 volts. If that's a cheapo 16 gauge extension cord. You will have about 13-15 percent voltage drop so you would need at least 120 volts coming in to the cord to keep the voltage at the distant end above the Progressive drop out voltage level.

I suspect your problem has no relationship to the transfer switch but power disconnect is occurring due to the Progressive detecting a low voltage condition. The Progressive contactor is the thunk you're hearing and not the transfer switch.

I think you probably need a shorter and/or fatter cord.
When seconds count, the police are only minutes away.

2019 Newmar Canyon Star 3627
2017 Jeep Wrangler JKU

10forty2
Explorer
Explorer
tropical36 wrote:
farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the transfer switch keeps clicking on an off

Check the voltage at the source with it off and then at the load side with it on. The difference is the voltage drop and probably insufficient to activate the transfer sw.
If the fridge is your only concern, then just power it up directly.


That's what I was thinking. Just open the access panel to the fridge and plug it directly in to shore power.
1999 Holiday Rambler Endeavor, 36' Gasser
Triton V10, Ford F53 Chassis
-----------------------------------------

tropical36
Explorer
Explorer
farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the transfer switch keeps clicking on an off

Check the voltage at the source with it off and then at the load side with it on. The difference is the voltage drop and probably insufficient to activate the transfer sw.
If the fridge is your only concern, then just power it up directly.
"We are often so caught up in our destination that we forget to appreciate the journey."

07 Revolution LE 40E_Spartan MM_06 400HP C9 CAT_Allison 3000.

Dinghy_2010 Jeep Wrangler JKU ISLANDER.

1998 36ft. National Tropi-Cal Chevy Model 6350 (Sold)

time2roll
Explorer II
Explorer II
farmingdad wrote:
Yes it does have the progressive low voltage on it , that is problay what it is thanks
Fridge is only 3 amps and should run fine with minimal drop. Even keeping the battery charged should be only one extra amp once the batteries are topped up. Should not have an issue. I highly suspect something else is running.

farmingdad
Explorer
Explorer
Yes it does have the progressive low voltage on it , that is problay what it is thanks

OLYLEN
Explorer
Explorer
The Gen itself has a delay to stabilize then connect for power, the transfer switch makes contact or switching when shore power is added. And if the Gen is on or started most revert to the Gen. With the Gen off and connecting with low voltage the transfer chatters trying to power the RV.

LEN

hohenwald48
Explorer
Explorer
RLS7201 wrote:
farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the tranfer switch keeps clicking on an off


The transfer switch is in the normally closed position to shore power. It makes no difference what the voltage is. The transfer switch should not be trying to switch unless it sees voltage from the generator.
Are you sure it was the transfer switch clicking?

Richard



If you have a protector unit, like a built in Progressive unit, it could be disconnecting due to low voltage. When it connects/disconnects it make a thunk similar to the thunk of a transfer switch. (Probably uses a similar contactor internally)
When seconds count, the police are only minutes away.

2019 Newmar Canyon Star 3627
2017 Jeep Wrangler JKU

RLS7201
Explorer
Explorer
OLYLEN wrote:
Think you have it backward, default is Gen, when you plugin the transfer switch makes the noise. And then the electrons flow.

LEN


No I had it correct. In the transfer switch's relaxed state it conducts from shore power. When the generator starts, the circuit board, in the transfer switch, starts timing down, when it finishes timing down it energizes the coil and pull the transfer switch to the generator. When both shore power and generator are available, then the generator will be dominate.

Richard
95 Bounder 32H F53 460
2013 CRV Toad
2 Segways in Toad
First brake job
1941 Hudson

MrWizard
Moderator
Moderator
30amp ? or 50 amp

my 50 has two relay contactors

one for shore, one for generator
neither one is engaged unless there is power on that line
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s

time2roll
Explorer II
Explorer II
I thought generator was secondary (normally open) as the switch has a delay for the generator to get up to speed.

BigRabbitMan
Explorer
Explorer
Default for my coach is the generator and if voltage from a cord drops it will switch. Had intermittent voltage drop in a campground once and my transfer box was switching back and forth.
BigRabbitMan
Gas to Diesel Conversion project
76 FMC #1046, Gas Pusher became a Diesel Pusher
Discussion thread on this site
"You're never too old to learn something stupid."

OLYLEN
Explorer
Explorer
Think you have it backward, default is Gen, when you plugin the transfer switch makes the noise. And then the electrons flow.

LEN

RLS7201
Explorer
Explorer
farmingdad wrote:
When I ran a 100 ft drop cord out to motor home to keep ref working the tranfer switch keeps clicking on an off


The transfer switch is in the normally closed position to shore power. It makes no difference what the voltage is. The transfer switch should not be trying to switch unless it sees voltage from the generator.
Are you sure it was the transfer switch clicking?

Richard
95 Bounder 32H F53 460
2013 CRV Toad
2 Segways in Toad
First brake job
1941 Hudson