hotjag1

Lake Chelan, Wa/Lake Havasu, Az.

Senior Member

Joined: 07/14/2002

View Profile



Good Sam RV Club Member


Posted: 06/16/19 08:30pm Link  |  Quote  |  Print  |  Notify Moderator

The smaller motorhome in my signature has a 5500w Generac generator that is not producing current at higher loads. The generator starts and runs fine when using the coffee maker or the microwave, but when I turn on the AC, the compressor will run for about 10 minutes and then the generator stops producing any current to the motorhome but the Gen does stay running.
If I shut the Gen off and restart it, it starts producing current again as long as I don't run the AC more than a few minutes.
Why would the Gen stop power after 10 minutes of using the AC?

* This post was last edited 06/20/19 10:24pm by hotjag1 *   View edit history


hotjag1
2003 40' Allegro Bus, 3 slides, 400hp 8.9 liter ISL Cummins

2000 24' Dynamax Isata


akrv

Green Valley , AZ

Senior Member

Joined: 02/02/2004

View Profile



Good Sam RV Club Member

Offline
Posted: 06/16/19 09:56pm Link  |  Quote  |  Print  |  Notify Moderator

Went to a rally in Cashmere WA it was a 100 degrees the whole time. Every one that had 5500 generacs would shutdown when the AC was running and air temp got over 98 degrees. Turns out there is a high temp oil switch maybe yours has same problem. Almost all the units were 98-2004


2005 Coachmen Concord 275DS
2004 Malibu Maxx LT

hotjag1

Lake Chelan, Wa/Lake Havasu, Az.

Senior Member

Joined: 07/14/2002

View Profile



Good Sam RV Club Member


Posted: 06/16/19 10:34pm Link  |  Quote  |  Print  |  Notify Moderator

akrv wrote:

Went to a rally in Cashmere WA it was a 100 degrees the whole time. Every one that had 5500 generacs would shutdown when the AC was running and air temp got over 98 degrees. Turns out there is a high temp oil switch maybe yours has same problem. Almost all the units were 98-2004


That's a good thought as it has been pretty hot here. Did the Gens quit running or stop producing power? Mine keeps running but power output stops.

way2roll

Wilmington NC

Senior Member

Joined: 10/05/2018

View Profile


Offline
Posted: 06/17/19 06:14am Link  |  Quote  |  Print  |  Notify Moderator

Since it continues to run, it sounds more like the ATS than the overheat shutdown. Does anything else other than the AC continue to run? Is there a code on the panel?

NRALIFR

Truck Camping Out West

Senior Member

Joined: 11/27/2005

View Profile



Posted: 06/17/19 06:52am Link  |  Quote  |  Print  |  Notify Moderator

Low oil level or pressure, and over temp will shut the engine down. That’s what those two sensors are protecting.

Maybe a self-resetting circuit breaker somewhere?

[emoticon][emoticon]


2001 Lance 1121 on a 2016 F450


hotjag1

Lake Chelan, Wa/Lake Havasu, Az.

Senior Member

Joined: 07/14/2002

View Profile



Good Sam RV Club Member


Posted: 06/17/19 11:09am Link  |  Quote  |  Print  |  Notify Moderator

way2roll wrote:

Since it continues to run, it sounds more like the ATS than the overheat shutdown. Does anything else other than the AC continue to run? Is there a code on the panel?


When the Gen cuts power, nothing in the coach works. When this happens, I checked with a meter and there is no power to the ATS. The odd thing is that when I personally shut down the Gen and then retart it a minute later, I have power to the coach again. I'm wondering if worn brushes or contacts would do this when a heavy load is put on the Gen.

D.E.Bishop

Eagle Rock, CA

Senior Member

Joined: 08/09/2001

View Profile



Good Sam RV Club Member

Online
Posted: 06/17/19 12:47pm Link  |  Quote  |  Print  |  Notify Moderator

From past experience I can tell you that if the brushes are not in contact with the slip rings your generator will shut down.

My suggestion is to first check the circuit breakers on the genny.


"I travel not to go anywhere, but to go. I travel for travel's sake. The great affair is to go". R. L. Stevenson

David Bishop
2002 Winnebago Adventurer 32V
Back to a 2006 Suzi GV
Roadmaster 5000
Roadmaster Invisibrake


sempka

Oklahoma

Full Member

Joined: 07/10/2016

View Profile



Good Sam RV Club Member

Offline
Posted: 06/17/19 06:48pm Link  |  Quote  |  Print  |  Notify Moderator

Generac parts for rv generators are getting hard to find. Generac has gotten out of the rv generator business. If you need parts they will refer you to another company that has limited parts for Generac rv gen sets.


2000 Holiday Rambler Admiral

hotjag1

Lake Chelan, Wa/Lake Havasu, Az.

Senior Member

Joined: 07/14/2002

View Profile



Good Sam RV Club Member


Posted: 06/17/19 07:31pm Link  |  Quote  |  Print  |  Notify Moderator

D.E.Bishop wrote:

From past experience I can tell you that if the brushes are not in contact with the slip rings your generator will shut down.

My suggestion is to first check the circuit breakers on the genny.


The circuit breakers aren't tripped, and as soon as I shut the Gen down and restart, I have power again. I have located a Generac repair facility about 3 hours from my home and have made an appointment to have them look at it on Thursday. Generac repair facilities are far and few between, but I will report what they find out.

I appreciate all of the comments and suggestions that I have received about this problem. Thank-you!

hotjag1

Lake Chelan, Wa/Lake Havasu, Az.

Senior Member

Joined: 07/14/2002

View Profile



Good Sam RV Club Member


Posted: 06/20/19 10:35pm Link  |  Quote  |  Print  |  Notify Moderator

Generac service center did a lot of testing and determined that when the GEN was under heavy load (AC) the voltage regulator would get warm and the voltage would increase. When that happened an internal resetting circuit breaker would open and cut power output from the GEN.

The voltage regulator under lighter loads such as coffee maker or microwave wasn't drawing enough power to heat up the voltage regulator as this only happened with the AC on. They replaced the voltage regulator and ran the AC for over an hour and everything worked as designed. $100 labor and $100 regulator and so far, so good.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Next

Open Roads Forum  >  Class A Motorhomes  >  All

 > Generac generator quits power output...UPDATE
Search:   Advanced Search

Search only in Class A Motorhomes


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2020 CWI, Inc. © 2020 Good Sam Enterprises, LLC. All Rights Reserved.