kmb1966

Lake Charles

Senior Member

Joined: 09/18/2005

View Profile


Offline
Posted: 07/23/19 02:33pm Link  |  Quote  |  Print  |  Notify Moderator

I have a 4 year old Dometic Penguin II air conditioner (non-heatpump unit) as the rear unit in a 2003 Newmar Dutchstar that is acting strange.
The unit in Fan Auto mode comes on when the thermostat is set below the set point as expected. But it will cut off (fan and compressor) briefly (5 seconds) and it has not yet reached the setpoint temp. Then it will come back on and continue to cool again. This unit has been doing this for several weeks while we have been on vacation. But now the unit is doing something slightly different now. It will come on, cool (45-49 degrees coming out of vents, 68-69 degrees on the intake vents) but will only cool for approximately 7-10 minutes and then the compressor cuts off, fan continues to run. Then the fan will continue to run for approx 10 minutes without compressor. Compressor will kick on and only run 3-5 minutes, and then cutoff again. This operating cycle continues until it eventually reaches the setpoint temp and finally the fan and compressor will turn off. This causes it to take a long time to cool off, and at times we will wake up hot in the middle of the night to find the fan on, but the compressor is not, and yet it has not reached the setpoint temp. In the Fan ON mode, basically the same thing happens. The unit will come on and cool, but then after 10 minutes or so the compressor disengages and only the fan runs but the setpoint temp has not yet been reached . I don't think this is normal behavior and I am unsure what the problem is.

Ranger Smith

Wherever the rig is parked

Senior Member

Joined: 05/13/2006

View Profile





Offline
Posted: 07/23/19 02:37pm Link  |  Quote  |  Print  |  Notify Moderator

Sounds like a capacitor going bad. I just had one that did the same thing. Compressor would cut off then come back on. Replaced run capn and no more issues.


Where we are now

Amateur Radio Operator WW1SS . . . Flex 6500 & Maestro, Flex 6400M Acom 1000, Icom 7100
Steve and Joy
2011 Itasca Meridian 40u . . . 2016 Lincoln MKX
The Doodles, Abbie & Abel
Baby and Kissie the Chihuahuas and Lucy the Biewere Yorkie


marcsbigfoot20b27

Phx

Senior Member

Joined: 08/24/2013

View Profile



Good Sam RV Club Member

Offline
Posted: 07/23/19 02:43pm Link  |  Quote  |  Print  |  Notify Moderator

I would bet it is freezing up/freeze sensor. Is the fan on high? How much humidity?

Chris Bryant

Arden, North Carolina

Senior Member

Joined: 03/26/2003

View Profile



Posted: 07/23/19 02:59pm Link  |  Quote  |  Print  |  Notify Moderator

Have you been on the roof to check it out? A hole in the shroud will cause that, allowing air to bypass the condenser. For this problem it would cycle on the overload.


-- Chris Bryant

Roger10378

Goodrich, MI.

Senior Member

Joined: 05/29/2008

View Profile



Good Sam RV Club Member

Offline
Posted: 07/23/19 03:37pm Link  |  Quote  |  Print  |  Notify Moderator

marcsbigfoot20b27 wrote:

I would bet it is freezing up/freeze sensor. Is the fan on high? How much humidity?


X2


2005 Cardinal 30TS
2007 Chevy 2500HD D/A

kmb1966

Lake Charles

Senior Member

Joined: 09/18/2005

View Profile


Offline
Posted: 07/23/19 05:49pm Link  |  Quote  |  Print  |  Notify Moderator

marcsbigfoot20b27 wrote:

I would bet it is freezing up/freeze sensor. Is the fan on high? How much humidity?


I'm not sure if this is what you are asking, but when I put the fan in the ON-HIGH position, the compressor and fan come on, unit cools for approx 7-10 minutes, then the compressor goes off and fan stays ON. Then after about 10 minutes, the compressor will come back on for about 5 minutes, then goes back off. This keeps on going this way until the setpoint temp has been reached.
Today outside temp is 80 degrees, humidity is 85%.

marcsbigfoot20b27

Phx

Senior Member

Joined: 08/24/2013

View Profile



Good Sam RV Club Member

Offline
Posted: 07/23/19 07:41pm Link  |  Quote  |  Print  |  Notify Moderator

Wait, 68-69 on the intake vents??????

How cold are you wanting the inside of your rig?
What is the thermostat set at?

kmb1966

Lake Charles

Senior Member

Joined: 09/18/2005

View Profile


Offline
Posted: 07/23/19 08:23pm Link  |  Quote  |  Print  |  Notify Moderator

marcsbigfoot20b27 wrote:

Wait, 68-69 on the intake vents??????

How cold are you wanting the inside of your rig?
What is the thermostat set at?


During the day I have it set to 75
At night I have it set to 70

The readings are from a laser thermometer, so that it was it reads IN and OUT.

DFord

Near St Louis, MO

Senior Member

Joined: 12/16/2001

View Profile





Offline
Posted: 07/23/19 09:42pm Link  |  Quote  |  Print  |  Notify Moderator

There could be a freezestat stuck between the coils of the evaporator causing this issue. And the capacitors are another possibility.

The freezestat prevents the indoor coil from frosting over and completely stopping the flow of air through the coil. When the compressor stops with the fan running, the ice melts and compressor restarts only to have the coil freeze up again.

If it's a capacitor, the internal overload on the compressor could be overheating and breaking the power for the motor until it cools.


Don Ford
2004 Safari Trek 31SBD (F53/V10 20,500GVW)
'09 HHR 2LT or '97 Aerostar MiniVan (Remco driveshaft disconnect) for Towed vehicles
BlueOx Aventa II Towbar - ReadyBrake Inertia Brake System


Chris Bryant

Arden, North Carolina

Senior Member

Joined: 03/26/2003

View Profile



Posted: 07/24/19 04:29am Link  |  Quote  |  Print  |  Notify Moderator

I don’t have my temperature/pressure charts, but iirc, with an outside temperature at 80 or below, the evaporator coil temp will be below freezing, so the freeze sensor is working as intended.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Next

Open Roads Forum  >  Tech Issues

 > Dometic Penguin II - cools, but compressor cuts on and off
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2020 CWI, Inc. © 2020 Good Sam Enterprises, LLC. All Rights Reserved.