This is just a curiosity question, I'm not getting shocked and I'm not planning on building a neutral ground plug.

I read on here about hot skin issues where a person is getting shocked by their RV and it's usually because the ground is broken somewhere in the shore power path.

I also read on here where people on generator need to create a neutral ground bond plug to trick their EMS into allowing power through.

The question then is does running a neutral ground plug cause a possible danger for a hot skin issue where the danger might not have existed without the plug?


2001 Suburban 4x4. 6.0L, 4.10 3/4 ton
2005 Jayco Jay Flight 27BH
1986 Coleman Columbia Popup.

LittleBill

Scranton, PA USA

Senior Member

Joined: 08/29/2003

View Profile


Offline
Posted: 08/07/19 12:12pm Link  |  Quote  |  Print  |  Notify Moderator

considering your house has neutral and ground bounded at the panel, its not a issue,

and considering there is no direct path to ground on a generator unless a ground rod is used, its even less of a risk.





PNW_Steve

Pacific Northwet & cold

Senior Member

Joined: 01/08/2014

View Profile


Offline
Posted: 08/07/19 01:30pm Link  |  Quote  |  Print  |  Notify Moderator

Neutral and ground should be bonded in one place. If you are plugged into shore power they wI'll be bonded at the panel.

If you are on generator or inverter power you need to make sure that you have a ground neutral bond at the power source.


2004.5 Dodge 3500 5.9 Cummins, NV5400, 5" turbo back stainless exhaust, Edger programmer & 22.5 Alcoa's
2002 Forest River 36 5th Wheel (staying home)
1992 Jayco 29 5th Wheel (Mexico veteran & headed back)
2002 "faux" Wanderlodge 40' My new toy....


road-runner

Oregon

Senior Member

Joined: 05/03/2015

View Profile


Offline
Posted: 08/07/19 02:03pm Link  |  Quote  |  Print  |  Notify Moderator

opnspaces wrote:


The question then is does running a neutral ground plug cause a possible danger for a hot skin issue where the danger might not have existed without the plug?
The only thing I can think of offhand is if the hot were to somehow become earth grounded, then using the bonding plug with a generator would make the rv frame hot. This would also happen with a built-in generator since it's already bonded. I don't see how this could happen unless there's a faulty device plugged into the RV or generator, sitting outside and making an earth ground. An unbonded generator supplies an extra level of protection from a situation like this. On the other hand it masks detection of the fault.


2009 Fleetwood Icon

Slownsy

USA

Senior Member

Joined: 01/16/2011

View Profile



Good Sam RV Club Member

Offline
Posted: 08/07/19 03:21pm Link  |  Quote  |  Print  |  Notify Moderator

What is the EMS and why the neutral and ground bonding? On generator.
Frank.


Frank
2012 F250 XLT
4x4 Super Cab
8' Tray 6.2lt, 3.7 Diff.

KD4UPL

Swoope, VA

Senior Member

Joined: 03/16/2008

View Profile



Good Sam RV Club Member

Offline
Posted: 08/07/19 03:43pm Link  |  Quote  |  Print  |  Notify Moderator

No, it does not cause any risk. When running an RV from a generator nothing is really grounded anywhere unless you drive a rod and nobody does that.
If anything, it's a safety measure so that a short to ground in the RV will actually trip the breaker on the gen. With no bond plug it wouldn't trip the gen breaker. So, you're safer with the bond plug.

wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile


Online
Posted: 08/07/19 04:31pm Link  |  Quote  |  Print  |  Notify Moderator

Hot Skin requires that the generator be earth grounded.

Normal wiring in an 30 amp RV the SKIN wants to be at 60 volts.. You can't draw much current but ti wants to be at 60 volts.. I can explain the reason but unless you have a background in electronics I'm not sure how well you will understand.

On a 50 amp RV plugged into 120 volts it's even higher Like 80. still low current though.

The bonding plug takes it to zero relative to neutral So it's safe Some devices need it. Some do not.


The reason

A device called a voltager divider..

Imagine the following DC circuit (I do not need I actually used it)

Battery 12 volt----Light bulb---X----Identical Light Bulb--- Ground

Now the voltage at X.. six volts Makes sense right (This is the SEE ME Day time Running Light system by the way, how it works. . Told you I used one)

Now.. for an AC circuit.
A capacitor is two pieces of conductive metal with an insulator (Even air) between them The symbol is --)|---

Now think about a length of ROMEX cable

There is a black wire next to a bare wire ( ---)|--- )

And there is a white wire on the other side of the bare wire ( ---)|--- )

Result is ---)|----G---|(---

60 volts at G.. Just like the 6 volts in the DC example

But very low current as they are very small Capicators.


Home is where I park it.
Kenwood TS-2000 housed in a 2005 Damon Intruder 377


time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 08/07/19 04:58pm Link  |  Quote  |  Print  |  Notify Moderator

Yes neutral-ground bond is perfectly safe for an independent, portable or on-board power source. Many generators and inverters bond the neutral and ground when producing power. Same as utility power has neutral-ground bonded at the source (meter).


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

opnspaces

San Diego Ca

Senior Member

Joined: 12/22/2004

View Profile


Offline
Posted: 08/07/19 06:17pm Link  |  Quote  |  Print  |  Notify Moderator

Thanks for trying to explain it to me. I think I'm slowly grasping it. Though I'm going to have to sit and mull it over for a while.[emoticon]


wa8yxm- I read your post a few times and then it hit me. When you're talking about 60v you're talking about an inductive current where the magnetic field from the electrons moving through the hot wire are creating current in the adjacent wire.

Then (and here's where I start to feel old) I remember running a test to prove this on the floor of my garage and posting it here on RV.net many years ago.

I can't find the post now, but I remember using a modified plug with only the hot wire and maybe a ground connected. Using a multimeter I could read 60v on the neutral wire.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Tech Issues

 > Is a neutral ground bond plug safe
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2020 CWI, Inc. © 2020 Good Sam Enterprises, LLC. All Rights Reserved.