Posted: 07/15/20 01:13pm Link  |  Quote  |  Print  |  Notify Moderator

My RVP 8000 roof air is drawing a lot of power, it's also vibrating. I suspicious that the motor is going out. Replacement motors are very cheap. Anyone have thoughts on this?

dougrainer

Carrolton, Texas

Senior Member

Joined: 06/11/2007

View Profile


Offline
Posted: 07/15/20 01:53pm Link  |  Quote  |  Print  |  Notify Moderator

1. Fan motors hardly ever pull enough amps to trip a breaker. Fans run about 2.5 amps max and you are on a dedicated 20 amp breaker
2. Vibration is caused by Impellor/Blade imbalance. This is usually caused by a Mud Insect nest on either the outside fan blade of the inside Impellor squirrel cage. Doug

time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 07/15/20 02:26pm Link  |  Quote  |  Print  |  Notify Moderator

Yes increased amp draw is an indication the compressor is failing. I believe the best option is to replace the entire upper unit. Get a clamp-on ammeter on the circuit and verify to specification.


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 07/15/20 04:12pm Link  |  Quote  |  Print  |  Notify Moderator

There are several things that cause excessive vibration and i've seen a few of 'em not all on my rig
One is a cracked or deformed fan or blower (On my dash air and on another person's RV) another is insect nests (my own) Rarley is it the motor

Also this will kick up the amps an amp or two

It will also reduce air flow
Which can seriously kick up the amps.

Another thing is a clogged air path. This can result in vibration as the air does some strange stuff. And if it is the CONDENSER it will drive up the internal heat in the system. this increases head pressure. Runs the amps up to the point of a breaker trip.

Inspection and cleaning fix most of that. Replace defective fans or blowers.


Home is where I park it.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times


houstonstroker

Houston, TX

Senior Member

Joined: 07/16/2003

View Profile



Good Sam RV Club Member


Posted: 07/16/20 03:31pm Link  |  Quote  |  Print  |  Notify Moderator

What is the voltage where you are parked? If the voltage goes down enough the amps will go up.


2016 Dynamax Force HD Super C

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Tech Issues

 > RVP roof air. Starting to through breakers.
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2021 CWI, Inc. © 2021 Good Sam Enterprises, LLC. All Rights Reserved.