CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile


Offline
Posted: 03/16/21 10:25am Link  |  Quote  |  Print  |  Notify Moderator

Specs don't necessarily reflect normal operation. Could be for fuses, heavy load startup, low AC voltage, temperature, power factor, etc.

60A*14.8V*1.2 (20% loss) = 1065W/120V = 9A or about half the gen rating.

Plus how often/long will it actually be charging at that rate?


2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob


BFL13

Victoria, BC

Senior Member

Joined: 02/15/2006

View Profile



Posted: 03/16/21 10:27am Link  |  Quote  |  Print  |  Notify Moderator

A single 27 will accept about 45 amps at 50% SOC and taper almost right away for its Absorption Stage. If you hit it with 60 amps all that happens is the amps will immediately drop to whatever the 27 will accept and taper from there.

That's with a flooded battery--don't do that with AGM or Si02--stick with their 27% charging limits--ie 27 amps on a 100AH batt or you can use your 55 amper on a pair of 100s. LFP can take it though.

ISTR a Honda 2000 spec is 13.3 amps at 120v for running output of 1600w (VA really)

I prefer the PowerMax line (same as Boondocker, a rebadged PowerMax) but the PD with Charge Wizard might be easier to operate if you are not ready to do manual voltage adjustments to suit your battery specs. (or you can chose the standard three-stage automatic mode if on shore power) If you are on shore power it doesn't matter about which converters--they all do about the same Float voltage.

Most converters at 75 amps and below are not power-factor corrected and their PFs are about 0.7, so you have to add that to what the generator will have to supply.

EG, as measured with a Trimetric and a Kill-A-Watt here is how it works for a 55 amp converter with battery accepting 56.8 amps and rising through 13.7 volts. (3000w Honda generator)

124.7 v, 11.06 a, 980w, 0.7PF, 1380VA (Kill-A-Watt )

So the Honda 1600 VA would supply that 1380VA. Same deal with a 75 amp converter needs the gen supplying 1700 VA, so the Honda 2000 would be a little overloaded. The Honda 2200 is rated for 1800VA though, so that would be ok with a 75 amper.

My B&S P2200 just barely runs my 75 amp converter which pulls 1700VA and the gen is rated at 1700VA.

You have a choice if the WFCO does run of leaving it in place and get a deck mount converter to work with the gen, or else replace the WFCO "lower portion" with a better converter.


1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

pinesman

virginia

Senior Member

Joined: 08/21/2006

View Profile


Offline
Posted: 03/16/21 10:41am Link  |  Quote  |  Print  |  Notify Moderator

Keep in mind that while your might not generator will not get above idle with the WFCO, putting in one of these better converters will cause your generator to speed up a little for a while, or at least that is my case with my Boondocker 55, 4 batteries and 2000w generator.

pulpwood007

Hemphill, TX

New Member

Joined: 05/25/2020

View Profile


Offline
Posted: 03/16/21 11:07am Link  |  Quote  |  Print  |  Notify Moderator

BFL13 wrote:

A single 27 will accept about 45 amps at 50% SOC and taper almost right away for its Absorption Stage. If you hit it with 60 amps all that happens is the amps will immediately drop to whatever the 27 will accept and taper from there.

That's with a flooded battery--don't do that with AGM or Si02--stick with their 27% charging limits--ie 27 amps on a 100AH batt or you can use your 55 amper on a pair of 100s. LFP can take it though.

ISTR a Honda 2000 spec is 13.3 amps at 120v for running output of 1600w (VA really)

I prefer the PowerMax line (same as Boondocker, a rebadged PowerMax) but the PD with Charge Wizard might be easier to operate if you are not ready to do manual voltage adjustments to suit your battery specs. (or you can chose the standard three-stage automatic mode if on shore power) If you are on shore power it doesn't matter about which converters--they all do about the same Float voltage.

Most converters at 75 amps and below are not power-factor corrected and their PFs are about 0.7, so you have to add that to what the generator will have to supply.

EG, as measured with a Trimetric and a Kill-A-Watt here is how it works for a 55 amp converter with battery accepting 56.8 amps and rising through 13.7 volts. (3000w Honda generator)

124.7 v, 11.06 a, 980w, 0.7PF, 1380VA (Kill-A-Watt )

So the Honda 1600 VA would supply that 1380VA. Same deal with a 75 amp converter needs the gen supplying 1700 VA, so the Honda 2000 would be a little overloaded. The Honda 2200 is rated for 1800VA though, so that would be ok with a 75 amper.

My B&S P2200 just barely runs my 75 amp converter which pulls 1700VA and the gen is rated at 1700VA.

You have a choice if the WFCO does run of leaving it in place and get a deck mount converter to work with the gen, or else replace the WFCO "lower portion" with a better converter.


Thanks, good info. This will be a deck mounted (stand alone) converter, not one housed in the power distribution box.

It sounds like the 45 amp converter would be fine for my group 27 lead acid battery, and run well on the EU2000. The only catch is that the 55 amp model is the same price on Amazon.

So. I guess the question is if the single 27 accepts max 45 amps at 50% charge level, will the converter charge output drop accordingly, and hence draw less current on the AC input side? I would think definitely yes since the DC output load has decreased, and I could probably calculate that using the power factor.

Obviously I'd like to go with the 55 amp model which I know the EU2000 would supply, but also have a little power left over to run lights and maybe TV in the trailer. Looks like I need to get the AmpClamp out and do a little measuring.

As far a manual adjustments, I have no problem with that. 99.9% of the time the 3 stage auto mode will be fine. I just want to have the option of locking in boost mode for rapid battery recharge when needed. I do like the remote pendant the PD offers, but again going into the PowerMax as seldom as I would be needing boost would be no issue.

Edit: Just spoke with PowerMax and found the 55 amp converter will draw 975 watts (under full load) from the generator. Looks like I'm golden!

* This post was edited 03/16/21 11:21am by pulpwood007 *

morley

British Columbia

Senior Member

Joined: 03/17/2010

View Profile



Good Sam RV Club Member

Offline
Posted: 03/16/21 11:09am Link  |  Quote  |  Print  |  Notify Moderator

klutchdust wrote:

Best Converter without a doubt. Plug and play, excellent customer service . Call them, tell them what you need. fixed my issues with my batteries boiling in my Class C.



Totally agree Best Converter is the way to go, very simple lower portion replacement of your WFCO. Did it myself and it works well. Randy at Best is the “Best” very helpful and will answer all of your questions if you have any. No more boiled batteries for me now also.


2008 Topaz F254SS 26 ft.
2009 Chevy Silverado, 2500HD, Duramax, Allison Tranny, 4x4, EC
250 watt solar panel system, BlueSky controller and remote


pulpwood007

Hemphill, TX

New Member

Joined: 05/25/2020

View Profile


Offline
Posted: 03/16/21 11:23am Link  |  Quote  |  Print  |  Notify Moderator

morley wrote:

klutchdust wrote:

Best Converter without a doubt. Plug and play, excellent customer service . Call them, tell them what you need. fixed my issues with my batteries boiling in my Class C.



Totally agree Best Converter is the way to go, very simple lower portion replacement of your WFCO. Did it myself and it works well. Randy at Best is the “Best” very helpful and will answer all of your questions if you have any. No more boiled batteries for me now also.


I've done business with Randy before. Agree, good guy. I can just save a few bucks on the same converter branded as PowerMax.

time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 03/16/21 11:36am Link  |  Quote  |  Print  |  Notify Moderator

The only trouble with PowerMax is the short absorption time. With 55+ amps the converter will hit the 14.6 volts fairly quick and then you get maybe 15 to 30 minutes at that voltage and you are only about 80% charged when the voltage drops to 13.6.

For a single battery deck mount I recommend the BD 1235CL at just 35 amps. This will get you closer to 90+% charged before the voltage drops. Or go with the PD9245 or PD9260 that will hold the boost voltage a full 4 hours.


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

pulpwood007

Hemphill, TX

New Member

Joined: 05/25/2020

View Profile


Offline
Posted: 03/16/21 11:48am Link  |  Quote  |  Print  |  Notify Moderator

time2roll wrote:

The only trouble with PowerMax is the short absorption time. With 55+ amps the converter will hit the 14.6 volts fairly quick and then you get maybe 15 to 30 minutes at that voltage and you are only about 80% charged when the voltage drops to 13.6.

For a single battery deck mount I recommend the BD 1235CL at just 35 amps. This will get you closer to 90+% charged before the voltage drops. Or go with the PD9245 or PD9260 that will hold the boost voltage a full 4 hours.


I don't think so. PowerMax specs show a switch that can change from three stage auto to manual, locking output at 14.6. One only needs to remember to switch back to auto after fast charging of battery. I do like the remote pendant on the PD. Just wouldn't use it much for the price difference.

PM on auto:14.6 vdc for 0.5 hrs, 13.6 for 12 hrs, then to 13.2.

time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 03/16/21 12:16pm Link  |  Quote  |  Print  |  Notify Moderator

Yes if you want to adjust the PM manually you are good to go. Sometimes hard to know the technical level of these requests.

BFL13

Victoria, BC

Senior Member

Joined: 02/15/2006

View Profile



Posted: 03/16/21 12:34pm Link  |  Quote  |  Print  |  Notify Moderator

I didn't check amazon etc but this is a good deal and shipping

https://www.boatandrvaccessories.com/pro........-amp-12-volt-power-supply-with-led-light

As mentioned, your battery will only accept the amps it can at that SOC and at that voltage, so yes get the 55 or even the 60 in case you get a second battery someday.

You need a flashlight and a small screwdriver to do the adjusments, and a voltmeter to watch while you twiddle the pot. You can use cut off ends of jumper cables (#8 or fatter gauge) in the terminals to make it a portable charger.

Looks like they forgot about the PF when telling you the watts---see my post above for the real draw on the gen with a 55 amper (it was with a PowerMax)

They get the 120v input right in their table at 11 amps.
11 x 120v = 1320

EDIT-- note 975 x 100/70 = 1393 which is closer to the 1380 I get.

https://powermaxconverters.com/wp-content/uploads/2019/02/PM3-Spec-Sheet.pdf

* This post was last edited 03/16/21 12:59pm by BFL13 *   View edit history

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Prev

Open Roads Forum  >  Tech Issues

 > Converter replacement
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2022 CWI, Inc. © 2022 Good Sam Enterprises, LLC. All Rights Reserved.