Will The EMS-PT50X 50amp EMS operate properly if plugged into 30amps? Need to know before I commit...No response from Progressive Ind.
2020 Keystone Cougar 26RBS "Pressure Relief 4"
2017 Silverado LTZ 6.2 4x4
MM2 USN 1970-75
USS Canisteo AO-99
USS Miller DE-1091
----------------------------------------------------------------------
"Knowledge is good". Emil Faber
|
Gdetrailer

PA

Senior Member

Joined: 01/05/2007

View Profile

|
I am going to take a stab that it won't allow power if you are only supplying power to only one of the "legs"..
Page 6 of the manual..
HERE
"Example:
The EMS shuts down power for low voltage on Line-1 and then power is
restored. "
In a nutshell it is supposed to not allow voltage to pass if it is below 104V.. Guessing that would also mean that BOTH L1 and L2 must have voltage higher than 104V..
Page 5 seems to indicate that both L1 and L2 need voltages higher than 104V..
"NOTE:
If the display indicates an error code other than
E 0 or E 10, the EMS will not allow power to the RV. "
Now if your 30A 120V adapter were to supply voltage to both L1 and L2 then it "might" work but if unit is looking for L2 to be 180 degrees out of phase (the way it should be) then I suspect the unit won't pass voltage on to the trailer..
But, hey, you might get lucky and the EMS doesn't care if L1 and L2 are in phase..
All you can do is try it with the EMS and if it doesn't work just remove it or bypass it?
|
CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile

Offline
|
Yes with the standard 30/50 RV adapter. Aspects of the above post are incorrect, as the unit doesn't know or detect any aspect of 120/240V power, only that both legs have 120V within specs.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland
Bob
|
CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile

Offline
|
BTW The 120/240V 50A is SINGLE PHASE, it's a common misconception that it's 2 phase, etc.
Split phase is a reasonable description.
|
Gdetrailer

PA

Senior Member

Joined: 01/05/2007

View Profile

|
CA Traveler wrote: BTW The 120/240V 50A is SINGLE PHASE, it's a common misconception that it's 2 phase, etc.
Split phase is a reasonable description.
![rolleyes [emoticon]](https://forums.goodsamclub.com/sharedcontent/cfb/images/rolleyes.gif)
Connect L1 and L2 together on a proper 120/240 circuit and see what happens..
L1 and L2 are 180 degrees "out of phase" compared to each other and even the neutral and that IS correct.
When L1 is going in positive direction L2 is going in a negative direction. When L1 is going negative the L2 is going positive.
And there is ZERO "wrong" with what I posted.
The problem you have is "semantics".
There are 30A to 50A dogbones that only supply L1 with 120V connection and there are 30A to 50A dogbones that will connect both L1 and L2 to the single 120V 30A power source..
As I told the OP, all they can do is try it, if their dogbone does not connect both L1 and L2 together then their EMS will not allow voltage to pass..
However a REAL "EMS" in theory should not allow ANY voltage pass that has the exact same direction waveform on L1 and L2 as that is a violation..
|
|
afidel

Cleveland

Senior Member

Joined: 12/23/2016

View Profile

Offline
|
I can't answer definitively, but I can say that a EMS-HW50C works just fine with a Camco 30->50 dogbone and also with a Camco 20->30 with the 30->50 dogbone.
2019 Dutchman Kodiak 293RLSL
2015 GMC 1500 Sierra 4x4 5.3 3.42 full bed
Equalizer 10k WDH
|
ScottG

Bothell Wa.

Senior Member

Joined: 02/25/2005

View Profile

|
Lots of wrong info above. Suffice to say, the answer to your question is YES, the 50A unit will work fine on 30A (or 20A or 15A).
|
bolljl

Fulltimer

New Member

Joined: 02/23/2018

View Profile


Good Sam RV Club Member
Offline
|
"YES, the 50A unit will work fine on 30A"
total agree we have been using our EMS on 30A for last 10 years
2015 RAM LongHorn 3500 Dually 4X4 CUMMINS
2013 Lifestyle LS35SB, MORryde IS System
AIRSAFE, Air Hitch
|
dodge guy

Bartlett IL

Senior Member

Joined: 03/23/2004

View Profile

Offline
|
Yes, I just installed a Watchdog today. The system doesn’t know that you are splitting the power coming in. It just wants to see 2 120V circuits and a good ground and neutral. The only thing you have to watch (the EMS will do it too) is how many amps you are pulling. It will shut down early if it sees the voltage too low.
Wife Kim
Son Brandon 17yrs
Daughter Marissa 16yrs
Dog Bailey
12 Forest River Georgetown 350TS Hellwig sway bars, BlueOx TrueCenter stabilizer
13 Ford Explorer Roadmaster Stowmaster 5000, VIP Tow>
A bad day camping is
better than a good day at work!
|
Bobbo

Wherever I park

Senior Member

Joined: 09/16/2007

View Profile


Good Sam RV Club Member
Offline
|
Gdetrailer wrote:
Connect L1 and L2 together on a proper 120/240 circuit and see what happens..
L1 and L2 are 180 degrees "out of phase" compared to each other and even the neutral and that IS correct.
When L1 is going in positive direction L2 is going in a negative direction. When L1 is going negative the L2 is going positive.
And there is ZERO "wrong" with what I posted.
The problem you have is "semantics".
There are 30A to 50A dogbones that only supply L1 with 120V connection and there are 30A to 50A dogbones that will connect both L1 and L2 to the single 120V 30A power source..
As I told the OP, all they can do is try it, if their dogbone does not connect both L1 and L2 together then their EMS will not allow voltage to pass..
However a REAL "EMS" in theory should not allow ANY voltage pass that has the exact same direction waveform on L1 and L2 as that is a violation..
https://en.wikipedia.org/wiki/Split-phase_electric_power
Never too late to learn something.
Bobbo and Lin
2017 F-150 XLT 4x4 SuperCab w/Max Tow Package 3.5l EcoBoost V6
2017 Airstream Flying Cloud 23FB
|
|