stevenal

Newport, OR, USA

Senior Member

Joined: 03/16/2004

View Profile


Offline
Posted: 06/21/21 06:13pm Link  |  Quote  |  Print  |  Notify Moderator

ktmrfs,
And I continue to spend my life in the power delivery industry. Our bible is ANSI (American National Standards Institute) C84.1 when it comes to voltage. It spells out two ranges A and B, with A being the range to meet the majority of the time. Each range includes service voltage (what we care about) plus utilization voltage (at the receptacle.) None of this works out to 10%, but can be approximated by 5 at the service. If your electronics meet a wider range, that's good. Maybe an excursion into range B won't kill them.

I see you are in Portland. Perhaps you've heard of PGE.
https://www.pge.com/includes/docs/pdfs/m........tatus/powerquality/voltage_tolerance.pdf

The NEMA standard is +/- 10, but starts at 115 nameplate instead of the 120 nominal used by ANSI.


'18 Bigfoot 1500
Torklifts and Fastguns
'17 F350 Powerstroke Supercab SRW LB 4X4

ktmrfs

Portland, Oregon

Senior Member

Joined: 06/22/2005

View Profile


Offline
Posted: 06/21/21 07:13pm Link  |  Quote  |  Print  |  Notify Moderator

stevenal wrote:

ktmrfs,
And I continue to spend my life in the power delivery industry. Our bible is ANSI (American National Standards Institute) C84.1 when it comes to voltage. It spells out two ranges A and B, with A being the range to meet the majority of the time. Each range includes service voltage (what we care about) plus utilization voltage (at the receptacle.) None of this works out to 10%, but can be approximated by 5 at the service. If your electronics meet a wider range, that's good. Maybe an excursion into range B won't kill them.

I see you are in Portland. Perhaps you've heard of PGE.
https://www.pge.com/includes/docs/pdfs/m........tatus/powerquality/voltage_tolerance.pdf

The NEMA standard is +/- 10, but starts at 115 nameplate instead of the 120 nominal used by ANSI.


probably a case of source tolerance spec vs. equipment tolerance voltage spec. With the ANSI source tolerance A & B and a 10% equipment tolerance pretty much assured equipment will operate with source tolerances at the limit along with unexpected drops in the wiring system, especially when it comes to the low voltage end where most equipment runs into trouble.


2011 Keystone Outback 295RE
2004 14' bikehauler with full living quarters
2015.5 Denali 4x4 CC/SB Duramax/Allison
2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!


Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 3  
Prev

Open Roads Forum  >  Tech Issues

 > Honda 2200i Experts??
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2021 CWI, Inc. © 2021 Good Sam Enterprises, LLC. All Rights Reserved.