Are Ground Bonding Plugs required for Each Inverter/Genny?

Baja_Man
Explorer
Explorer
I am installing a new Progressive Industries hard wired EMS (EMS-HW30C).

I want to use a ground-neutral bonding plug on inverters/gennys to avoid using my by-pass function.

I plan on using my two Champion 2500W Dual Fuel inverters combined, using the Champion 30AMP ParaLINK Parallel kit.

Will each inverter/genny need its own plug or will one plug on one them suffice?

Thanks!
2023 GMC, 3500HD, Crew Cab, 6.6L Gas/6 Speed Auto, 4X4, Standard Bed; SRW
2011 Outback 250RS - Anniversary Edition
Equal-i-zer 10K
18 REPLIES 18

BFL13
Explorer II
Explorer II
Good catch, DrewE

https://bsintek.basco.com/BriggsDocumentDisplay/default.aspx?filename=ngjpyNY.p9ZVj5K1w

Page 22 of that has the wiring diagram, where it seems the ground for the receptacle goes to GT and so does what could well be the chassis ground.

EDIT--the thing also to GT in that diagram appears to be the paralleling connection, which has three pins to it. You see the plugs on the two cords from the kit here--they are sort of triangular and go in the same shaped receptacle on the gen.( I looked at mine under its cover flap--three holes for prongs) I do not have a wiring diagram for the kit.

So it seems one of the kit three prongs goes to GT

https://www.briggsandstratton.ca/na/en_ca/product-catalog/portable-generators/inverter-parallel-kit....

Glad we got that cleared up! Gads!
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

DrewE
Explorer
Explorer
BFL13 wrote:
My B&S P2200 portable inverter gen manual says, "--the AC stator winding is isolated from the grounding fastener and the AC receptacle ground pins. On a floating neutral generator the AC receptacle ground pins are not functional. Electrical devices, such as a GFCI, requiring a functioning ground pin will not operate."


That says nothing about the ground pin being isolated from the grounding fastener; those are indeed tied together. It's just saying (in a rather confusing, roundabout way) that the neutral--the stator winding--is not bonded to the two ground connections, but rather isolated from them.

I have no idea why they suggest a GFCI requires a functioning ground pin to operate. A GFCI specifically does not need a ground to operate. In fact, using a GFCI is one acceptable way, I think the only one permitted by the NEC, to install a receptacle accepting a three-prong grounded plug in an ungrounded two-wire AC branch circuit.

BFL13
Explorer II
Explorer II
My B&S P2200 portable inverter gen manual says, "--the AC stator winding is isolated from the grounding fastener and the AC receptacle ground pins. On a floating neutral generator the AC receptacle ground pins are not functional. Electrical devices, such as a GFCI, requiring a functioning ground pin will not operate."
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

2112
Explorer II
Explorer II
wnjj wrote:
BFL13 wrote:
In the link for the Link it shows the yellow wires going to each gen's chassis ground lug.

How does the chassis ground for the gen connect to the gen's receptacles' neutrals by using the bonding plug unless the gen's chassis is connected to the receptacles' grounds?

Is that what wnjj meant above?

Yes, the ground pins on the 20A receptacle are connected internally to the ground lug, which is where you attach the parallel kit ground.
I just verified this on all four of my Champions, one being an inverter model. The receptacle ground prong is tied to the external ground lug on all of them. He will connect the yellow/green striped ground wire to the ground lug and plug a bonding plug into any receptacle on either generator. This will bond ground to neutral on all receptacles. You want to bond at only 1 point.
2011 Ford F-150 EcoBoost SuperCab Max Tow, 2084# Payload, 11,300# Tow,
Timbrens
2013 KZ Durango 2857

BFL13
Explorer II
Explorer II
wnjj wrote:
BFL13 wrote:
In the link for the Link it shows the yellow wires going to each gen's chassis ground lug.

How does the chassis ground for the gen connect to the gen's receptacles' neutrals by using the bonding plug unless the gen's chassis is connected to the receptacles' grounds?

Is that what wnjj meant above?

Yes, the ground pins on the 20A receptacle are connected internally to the ground lug, which is where you attach the parallel kit ground.


See my edit from the B&S manual above though.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

wnjj
Explorer II
Explorer II
BFL13 wrote:
In the link for the Link it shows the yellow wires going to each gen's chassis ground lug.

How does the chassis ground for the gen connect to the gen's receptacles' neutrals by using the bonding plug unless the gen's chassis is connected to the receptacles' grounds?

Is that what wnjj meant above?

Yes, the ground pins on the 20A receptacle are connected internally to the ground lug, which is where you attach the parallel kit ground.

BFL13
Explorer II
Explorer II
In the link for the Link it shows the yellow wires going to each gen's chassis ground lug.

How does the chassis ground for the gen connect to the gen's receptacles' neutrals by using the bonding plug unless the gen's chassis is connected to the receptacles' grounds?

Is that what wnjj meant above?

My B&S P2200 portable inverter gen manual says, "--the AC stator winding is isolated from the grounding fastener and the AC receptacle ground pins. On a floating neutral generator the AC receptacle ground pins are not functional. Electrical devices, such as a GFCI, requiring a functioning ground pin will not operate."
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Bobbo
Explorer II
Explorer II
wa8yxm wrote:
As I understand it the parallel link has only two wires to each generator. Thus you will need to bond at the 30 amp outlet in the P-link.

I don't know about the Champion paralleling system, but the Honda paralleling system has 3 wires between the generators. It bonds the Hot, Neutral, and Ground. The bonding plug can go in any outlet as long as that outlet is on one of the generators.

And no, you do not need a bonding plug on each generator. One, on either generator, is sufficient.

ON EDIT: I just looked up the Champion parallel kits. They, also, have 3 wires. They have Hot, Neutral, and Ground.
Bobbo and Lin
2017 F-150 XLT 4x4 SuperCab w/Max Tow Package 3.5l EcoBoost V6
2017 Airstream Flying Cloud 23FB

2112
Explorer II
Explorer II
You need only 1 plugged into either genny. This will bond the yellow/green wires to either the red or black wires on both gennys. I don't know which is neutral.

You can verify this by plugging your bonding plug into either genny and measure resistance from the ground to neutral on either receptacle on the paralink. It should measure close to 0. Unplug your bonding plug and resistance should go high. All this with it powered Off of course.
2011 Ford F-150 EcoBoost SuperCab Max Tow, 2084# Payload, 11,300# Tow,
Timbrens
2013 KZ Durango 2857

wa8yxm
Explorer III
Explorer III
As I understand it the parallel link has only two wires to each generator. Thus you will need to bond at the 30 amp outlet in the P-link. Easiest way (if said assembly is not molded) is to open the outlet assembly and add a jumper.. Just make sure you jumper the PROPER (Neutral/Ground) pins.

Actually with inverter generators the Surge Guard is not needed so you an use the bypass mode safely.

But there is still a good reason to bond.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

wnjj
Explorer II
Explorer II
BFL13 wrote:
Baja Man wrote:
BFL13 wrote:
OP is asking about plugging into gens, but the two receptacles are in the paraLink.


The neutral-grounding plugs I am referring to are plugged into the inverters 120V receptacle


I have seen the bonded 15a adapters used for that and you would have one on the shore power cord plug. You say you will be using the parallel kit, so you will be plugging into one of the two 30a paraLink receptacles depending on your plug type, not into one of the gens.

Do you intend to have a 30a adapter modified to be bonded? Very confusing.

Heโ€™s planning to plug the RV into the paraLink kit but the bonding plug into one of the 120V receptacles on one of the generators.

The answer is it will work fine so long as the ground wire (I.e. the screw loop terminal) from the paraLink is connected to the ground lug on the generator with the bonding plug.

All bonding does is connect the green ground wire to the neutral. Once all neutrals are connected to each other and all grounds are connected to each other bonding can be done on either generator or at the unused the paraLink receptacle.

bob213
Explorer
Explorer
When I parallel my Hondas it only takes 1 (one) bonding plug. Either generator and your EMS will see a common ground.
You can avoid reality, but you cannot avoid the consequences of avoiding reality โ€“ Ayn Rand

BFL13
Explorer II
Explorer II
Baja Man wrote:
BFL13 wrote:
OP is asking about plugging into gens, but the two receptacles are in the paraLink.


The neutral-grounding plugs I am referring to are plugged into the inverters 120V receptacle


I have seen the bonded 15a adapters used for that and you would have one on the shore power cord plug. You say you will be using the parallel kit, so you will be plugging into one of the two 30a paraLink receptacles depending on your plug type, not into one of the gens.

Do you intend to have a 30a adapter modified to be bonded? Very confusing.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Baja_Man
Explorer
Explorer
BFL13 wrote:
OP is asking about plugging into gens, but the two receptacles are in the paraLink.


The neutral-grounding plugs I am referring to are plugged into the inverters 120V receptacle
2023 GMC, 3500HD, Crew Cab, 6.6L Gas/6 Speed Auto, 4X4, Standard Bed; SRW
2011 Outback 250RS - Anniversary Edition
Equal-i-zer 10K