Teleman wrote: I put circuit breakers on both sides of the charger too. I'm pretty confident I won't have any trouble. Circuit breakers and fuses are very imprecise devices. A batch of 60a breakers/fuses of the same type, from the same manufacturer, may open at 70a, 85a, or even higher. It's wishful thinking to assume a 60a breaker/fuse is going to open at 61a. Breakers/fuses are primarily designed to protect in the event of a short or massive overload condition. They don't have the precision necessary to effectively protect an alternator or battery from all over-current conditions.
BTW, the Redarc instruction manual (pg 10) states it does not recommend the use of self-resetting circuit breakers. They recommend the use of low-resistance MIDI fuses.
|
Teleman

Clayton, CA, USA

Senior Member

Joined: 08/11/2004

View Profile

Offline
|
otrfun wrote: Teleman wrote: I put circuit breakers on both sides of the charger too. I'm pretty confident I won't have any trouble. Circuit breakers and fuses are very imprecise devices. A batch of 60a breakers/fuses of the same type, from the same manufacturer, may open at 70a, 85a, or even higher. It's wishful thinking to assume a 60a breaker/fuse is going to open at 61a. Breakers/fuses are primarily designed to protect in the event of a short or massive overload condition. They don't have the precision necessary to effectively protect an alternator or battery from all over-current conditions.
BTW, the Redarc instruction manual (pg 10) states it does not recommend the use of self-resetting circuit breakers. They recommend the use of low-resistance MIDI fuses.
They are not self resetting.
|
otrfun

On The Road

Senior Member

Joined: 09/08/2012

View Profile


Good Sam RV Club Member
|
noteven wrote: . . . DC DC probably has some control around overloading the alternator.
Especially REDARC equipment- Australia has been a decade or two ahead of north North America using on board charging equipment in campers and trucks operating in remote regions. Outside of input/output connections and a trigger input to turn the unit off and on, there are no other connections or sensors on a Renogy dc to dc charger that would relay any info about an alternator's condition, load or output rating. I've briefly read through the 25a/40a Redarc manual and I believe this is also true for the Redarc.
There are a number of ways to program the *output* of a dc to dc charger to protect and properly charge the battery; however, very few options (if any) to regulate the *input* load to protect the alternator (the only exception is the half-power mode on the Renogy).
This is why choosing a dc to dc charger with the proper current rating is important (in respect to alternator load).
|
otrfun

On The Road

Senior Member

Joined: 09/08/2012

View Profile


Good Sam RV Club Member
|
Teleman wrote: otrfun wrote: Teleman wrote: I put circuit breakers on both sides of the charger too. I'm pretty confident I won't have any trouble. Circuit breakers and fuses are very imprecise devices. A batch of 60a breakers/fuses of the same type, from the same manufacturer, may open at 70a, 85a, or even higher. It's wishful thinking to assume a 60a breaker/fuse is going to open at 61a. Breakers/fuses are primarily designed to protect in the event of a short or massive overload condition. They don't have the precision necessary to effectively protect an alternator or battery from all over-current conditions.
BTW, the Redarc instruction manual (pg 10) states it does not recommend the use of self-resetting circuit breakers. They recommend the use of low-resistance MIDI fuses. They are not self resetting. The "self-resetting" comment was more for general consumption. However, I do believe Redarc's recommendation to use MIDI fuses might be something you may want to consider (vs. using circuit breakers).
* This post was
edited 11/22/21 09:45am by otrfun *
|
noteven

Turtle Island

Senior Member

Joined: 02/13/2011

View Profile

|
otrfun wrote: noteven wrote: . . . DC DC probably has some control around overloading the alternator.
Especially REDARC equipment- Australia has been a decade or two ahead of north North America using on board charging equipment in campers and trucks operating in remote regions. Outside of input/output connections and a trigger input to turn the unit off and on, there are no other connections or sensors on a Renogy dc to dc charger that would relay any info about an alternator's condition, load or output rating. I've briefly read through the 25a/40a Redarc manual and I believe this is also true for the Redarc.
There are a number of ways to program the *output* of a dc to dc charger to protect and properly charge the battery; however, very few options (if any) to regulate the *input* load to protect the alternator (the only exception is the half-power mode on the Renogy).
This is why choosing a dc to dc charger with the proper current rating is important (in respect to alternator load).
I think otr is correct ^. I have a Renogy on the project shelf. It is a 40amp model. The literature states input amps are 60amps at 40amps output.
High output alternators are not super expensive if your oem one kicks the bucket..
|
|