Advice on replacing my IOTA battery charger for boondocking

opnspaces
Navigator
Navigator
I am looking for advice, or maybe just reassuring confirmation that what I am thinking is sound.
I'm looking for a three stage battery charger that I don't have to worry about. I just want to start the generator, plug in the shore power cord, let it run for a few hours and get the batteries back up to 90 percent.

I have a 2005 Jayco Jayflight 27BH travel trailer with a IOTA DLS-3045 load center (I have verified that IQ4 is not an option on this unit). I almost exclusively dry camp with two 6volt Costco batteries and a Honda EU2000i generator.

I was thinking about replacing my charger with an IOTA DLS-45 with IQ4. Not sure why I'm focusing on IOTA except that it's the same brand as the load center. With the IQ4 it is supposed to be a true 3 stage charger. IOTA DLS-45

My other thought based on years reading this form is something from Progressive Dynamics in the 92xx series. But the 92xx series appears to have a remote pendant that I have to use to put it into bulk mode which I want to avoid. Progressive Dynamics 92xx

I am thinking 45 amp so I don't need to upgrade the battery wiring.
I have plenty of room behind the load center for a deck mount charger.
Solar will probably be a few years off.

Two postings I found here that mention exactly what I'm thinking about.
Link 1
Link 2

What are your thoughts?
.
2001 Suburban 4x4. 6.0L, 4.10 3/4 ton **** 2005 Jayco Jay Flight 27BH **** 1986 Coleman Columbia Popup
44 REPLIES 44

otrfun
Explorer II
Explorer II
BFL13, just replied, thanks.

BFL13
Explorer II
Explorer II
otrfun--sent you a PM
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

BFL13
Explorer II
Explorer II
otrfun wrote:
BFL13 wrote:
My PowerMax converters (100a, 75a, 55a) have all met and exceeded their amp ratings (103, 76, 56). There are two main reasons for not reaching converter rating:

1. Using #8 output wiring. Needs #4. Their instructions are not clear about that.
2. Low 120v input. It runs but at lower amps . . .
When I used my 60a PowerMax, input voltage was 122v under full load. Output was connected to several different discharged batteries and dc loads with 3 ft. long, 2 gauge cables. Output current would never exceed 53-54a. Same loads connected to a PD converter produced rated current.

I'm not saying PowerMax converters in general do not produce their rated current. What I am saying it's possible PowerMax may have quality control commensurate with their pricing.


I have no way of knowing about that. You must be annoyed with your unit though. There is a warranty, but I remember with my busted Parallax, it was a hassle where I had to pay to ship it back to them on the off-chance they would find something wrong with it, etc. I chose not to bother. Don't know how it works with PowerMax.

Meanwhile, if the PD was not when using the same #2 cables as the PowerMax, might be worth checking the #2 connections. Must be an adapter to the lug to get it in the #4 converter terminal that could be the culprit.

Back in the day we had lots of posts about PDs not meeting rated amps and failing to hold constant amps in Bulk. Salvo used some graphs to show that eg. Then a guy posted his graph that showed his PD doing ok where he used short fat wire. I never have had a PD to do my own measurements.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

otrfun
Explorer II
Explorer II
BFL13 wrote:
My PowerMax converters (100a, 75a, 55a) have all met and exceeded their amp ratings (103, 76, 56). There are two main reasons for not reaching converter rating:

1. Using #8 output wiring. Needs #4. Their instructions are not clear about that.
2. Low 120v input. It runs but at lower amps . . .
When I used my 60a PowerMax, input voltage was 122v under full load. Output was connected to several different discharged batteries and dc loads with 3 ft. long, 2 gauge cables. Output current would never exceed 53-54a. Same loads connected to a PD converter produced rated current.

I'm not saying PowerMax converters in general do not produce their rated current. What I am saying it's possible PowerMax may have quality control commensurate with their pricing.

BFL13
Explorer II
Explorer II
My PowerMax converters (100a, 75a, 55a) have all met and exceeded their amp ratings (103, 76, 56). There are two main reasons for not reaching converter rating:

1. Using #8 output wiring. Needs #4. Their instructions are not clear about that.
2. Low 120v input. It runs but at lower amps

EG my 75 runs at 76 off generator, but at 67ish on long #12 cord from stick house.

Same thing with my old Parallax 4455 I had some years ago. It did 55 amps on #8 but did 60 amps on #4.

The PowerMax units I have all ramp up their amps on start-up as seen on the Trimetric, so they reach max amps a tad after getting going.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

otrfun
Explorer II
Explorer II
opnspaces wrote:
I know the PD has a decent following as it works for people. But I'm wondering how much of the higher cost is really goodwill or perceived value and not anything to do with reliability or longevity over any other brand.
Every PD converter I've owned has always produced their rated output within +/- 1a. I purchased a 60a PowerMax converter about 6 mo. ago to use in our home for various projects. The adjustable charge voltage was a big plus. However, it would never produce its rated output. Max current hovered around 53-54a. Probably not a deal breaker for a number of folks, but it's something worth noting. Based on a number of PowerMax reviews I've read, this appears seems to be a common occurrence.

otrfun
Explorer II
Explorer II
opnspaces wrote:
one last question for any of you who run an inverter generator. Currently my Honda 2000i basically idles when plugged in and charging. I assume this is because the charger is stuck at 13.6 volts.

If I go to a PD 45 or a PD 60 amp I'm assuming the generator is going to ramp up a bit and make some noise. Does your 60 amp charger cause the generator to really ramp up and put out some noise? Or does it still stay fairly low in the decibel range? . . .
Yup, at 13.6v not much of a load--maybe 3-4a.

The Honda 2000 just starts getting noticeably louder as its load approaches 8a. 7a or less, it's still relatively quiet. The PD 45a and 60a converters I've used draw 7-8a and 9-10a under full-load at 14.4v. The PD 45a will ramp up the Honda a bit (the 60a noticeably more), but not as much as it would running an a/c.

opnspaces
Navigator
Navigator
I finally decided on and purchased the Powermax unit. My thought was that all three are basically the same as automatic three stage chargers. But with the Powermax I can flip it to manual mode and crank it up to 16v to equalize the batteries from time to time. Now I may never actually do that. But I have the option and the unit was less expensive than the PD or IOTA.

Thanks everyone who posted here and gave me your input.
.
2001 Suburban 4x4. 6.0L, 4.10 3/4 ton **** 2005 Jayco Jay Flight 27BH **** 1986 Coleman Columbia Popup

Gdetrailer
Explorer III
Explorer III
opnspaces wrote:

I know the PD has a decent following as it works for people. But I'm wondering how much of the higher cost is really goodwill or perceived value and not anything to do with reliability or longevity over any other brand.


If you are looking for a "set and forget" converter, hands down the PD series will do that for you. I do like the lower storage voltage mode of the PD at 13.2V because my RV sits unused for long periods of time plugged into shore power. Very low water use which means I don't have to check the water levels every month as I would if I had a converter that only settled down to 13.6V.

PD should also switch to bulk mode automatically when you apply shore or gen with a partially depleted battery. I know mine does that.

PD does have one strike against it, that is the PF or power factor is not as ideal which means it tends to draw a bit more power than other same amperage other brands. That can be an issue with using a smaller generator. A PD9160/PD9260 can draw more than 1000W at full output because of the PF. May be a bit close with your 2000W gen if you have other 120V items running. For that reason some folks have used a lower amperage PD with small gens.

Iota because of it's higher voltages might deliver a slight advantage to charging a bit faster, it takes more voltage to push more amps back into your battery.. However, the battery will tend to self limit just how much it will accept so any advantage there sort of depends on your type and size of battery.

Both PD and Iota are pretty much set and forget, in most cases, should never have to force modes, just allow them to do their jobs and all will be good.

If you have the need to constantly tinker with charging your batteries then something like the Power max which has the means of manually adjusting the voltage might be your ticket.. Some folks love to tinker with batteries as a hobby (battery maintenance hobby) and some like myself would rather spend time doing other hobby things..

pianotuna
Nomad II
Nomad II
opspaces,

Since they are sulfated I'd try to recover them.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

BFL13
Explorer II
Explorer II
OP wants to do 50-90s. A 60 amper on a 220AH bank does constant 60 and reaches Vabs at about 70% SOC and amps will then taper for the Absorption Stage.

So your gen will slow down then as amps taper and you can't use that as a marker for when to stop the recharge. You have to keep going until you get to 90% SOC.

45Amps on 220AH will do Bulk at 45 and reach Vabs at about 76%SOC and amps then taper with the gen then slowing down.

Even so the 60 amper will do the 50-90 in less time because it was doing 60 instead of 45 for the 50-70 and then its amps taper but from a higher level for the 70-76. They are equal in time for the 76-90 but the 60 holds its shorter time overall.

It must be time to inflict my ugly graph on everyone again! ๐Ÿ™‚

1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

BFL13
Explorer II
Explorer II
I am a shameless PowerMax fan. Been using them for ten years now.

Your 45 amper LK is $117 with free shipping here once they get more in.

https://www.boatandrvaccessories.com/products/powermax-pm3-45lk-45-amp-12-volt-power-supply-with-led...
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

time2roll
Explorer II
Explorer II
IOTA should not see over 14.6 for 15 minutes maximum. No harm in that and time to call done for the generator. Then 14.2 and eventually 13.6 float if you continue. Cycles back to boost once a week if power is continuous.

Or is this 13.6/13.4 new?

opnspaces
Navigator
Navigator
Interesting on the 20%c vs .125c (assuming that correlates to 12.5%c) I won't pretend to understand much of this battery charging. But I've read enough of your posts to think that 20%c is probably taxing on the batteries. If there is truly only 15 minutes charging difference between a 45 and 60 amp unit I'll probably go with the 45 amp.

So now my decisions are the PD costs $215 from bestconverters.com It charges at 14.4/13.6/13.2. The PD has the pendant that I can use to force into bulk mode for 4 hours if I want to.

The Powermax is $170 (on the Powermax website) It charges a 14.6/13.6/13.2. the Powermax does not have a pendant, but I can manually adjust the output up to 16.5 volts to equalize. This is done at home with a multimeter and a screwdriver which I'm more than capable of.

The IOTA with IQ4 is $160 from Bestconverters.com. It looks like the IOTA outputs 14.8/13.6/13.4 I think I'm ruling out the IOTA because if the higher bulk and float levels.

I know the PD has a decent following as it works for people. But I'm wondering how much of the higher cost is really goodwill or perceived value and not anything to do with reliability or longevity over any other brand.

Does anybody recall or have any thoughts on the reliability of the Powermax line? I don't recall any real negative posts on here so it seems good. But at the same time I don't want to buy the Harbor Freight equivalent of the converter world.
.
2001 Suburban 4x4. 6.0L, 4.10 3/4 ton **** 2005 Jayco Jay Flight 27BH **** 1986 Coleman Columbia Popup