We have 6 200 watt panels on the roof of our 5th wheel. Considering adding 1 or 2 more panels for those cloudy days.
Our 6 panels are arranged as 3 in series, 2 strings parallel. Our Victron MPPT controller is the 150/100. The manual says 100 amps and 150 volts are max and mentions a "nominal" of 1450 watts. Our solar system company says we can go to 8 panels in a 4 series, 2 parallel configuration. But I'm a little leery.
We could add a 100 watt panel to each string, making 1400 watts total. But do the 2 parallel sets have to be of equal wattage? Could I just add one 200 watt panel to one of the series strings? I realize that would create unequal voltages, but MPPT controllers convert the voltage anyway. Think about what happens when one panel gets shaded.
Thoughts and opinions?
Bill & Linda
Arizona
2019 Dodge Laramie 3500 dually 4x4 diesel
Hensley Trailer Saver BD5 hitch
2022 Grand Design Solitude 378MBS
1600 watts solar, 3kw inverter/charger, 3 206AH LiFePo4 batteries
|
3 tons

NV.

Senior Member

Joined: 03/13/2009

View Profile

Offline
|
If I understand you correctly, If you were to add one more 200w panel to say one of the existing series strings, assuming that the two paralleled strings outputs are tied together before entering the controller, the string with the now higher voltage would simply default to (or equalize with…) the voltage of the opposite string, thus no net increase in voltage…
3 tons
|
ktmrfs

Portland, Oregon

Senior Member

Joined: 06/22/2005

View Profile

Offline
|
Based on my experience I'll make the following comments.
1) parallel panels or strings should all be the same or close to the same string voltage, each panel or string can have different current rating and the MPPT controller will accomidate.
2) All panels in a series string should have the same or similar current rating (power). The string will be limited to the lowest current output of the panel in the string.
so based on your setup adding a 100W panel to a series string is not a good idea your limiting the current from a string, nor is adding a 200W panel to only one string, now you have parallel strings with different total voltage which the controller will likely have a fit with.
Now what to do? well you could add a couple or maybe 3 200 or 100W panels in series and run them to another MPPT controller and parallel controller output to the battery. check and see if the system allows parallel controllers
this is basically what I have on my trailer. roof has 3 200W panels in parallel to a Mppt controller (Midnite solar) and up to 4 200W portable panels I can use wired to another of the same controller. with the midnite solar system one controller is the master (roof) and the other the slave (portable). Master determines which mode the system should be in, bulk, float etc. and sets the slave to the same setting so both controllers are giving the same charge profile.
Depending on how far my portable run is and how much (or little) shade panels see I wire the portable panels in series or parallel, or a series parallel combo.
Have used this for years and it works great.
2011 Keystone Outback 295RE
2004 14' bikehauler with full living quarters
2015.5 Denali 4x4 CC/SB Duramax/Allison
2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!
|
CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile

Online
|
For maximum results the 100 and 200 panels in series must have the same amp rating ie Imp. For the 2 parallel strings the 2 strings should be same voltage ie Vmp. Best to use the same panels.
MPPT does convert the panel voltage/amps (power) to the battery voltage/amps. The problem with a mismatched parallel pair is he loss of overall power.
Find out how your contoller handles more that 1450W. Mine limits the amps when over panneled. Plus you are not likely to ever reach the maximum watts as a bright clear day with the panels pointed directly at the sun is required. So depending upon the over panel answer add 2x 200W OR a second controller with 400W.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland
Bob
|
time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile


Good Sam RV Club Member
|
Parallel needs to be equal voltage. Series needs to be equal in amps. 4s2p configuration will work fine.
2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up
|
|
CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile

Online
|
A little more techincal: For panels in series with different amp rating the entire string amp rating will be equal to the lowest panel amps and the string voltage will be the total voltage of all of the panels.
For panel strings in parallel the voltage will be the lower of the 2 strings. Adding a single panel to one string will not be useful.
|
Cptnvideo

Arizona - most of the time

Senior Member

Joined: 11/05/2006

View Profile

Offline
|
Excellent answers and I appreciate the feedback.
|