Posted: 07/16/22 10:48am Link  |  Quote  |  Print  |  Notify Moderator

time2roll wrote:

50 amp fuse close to the battery or power source. I agree with #8 unless the distance is long go #6 wire.


Fuse to the wire size, the idea is to protect the wire not the device hung on the wire.

SEE HERE

"Why use a fuse?

A fuse provides a safe and cost effective way to protect an electrical device or installation from electrical overloads which could damage components or wiring and potentially cause a fire."


Basically you want the fuse to blow out in a controlled manor well before the entire wire becomes a fuse.

Per HERE

"Fuses normally protect wires from burning and setting fire to things"

Per HERE

"When specifying a fuse for an after-market application, the key consideration is that the fuse should be the weakest point (i.e. lowest rated component) so that it always blows before any damage occurs to other parts of the electrical circuit. However, you also do not want the fuse to keep blowing under normal operation (known as a nuisance blow), so the two elements to consider are:

The current rating of the smallest cable in the circuit
The current draw on the circuit under normal expected operating conditions

The fuse rating should lie somewhere between these two values to allow normal operation but blow on overload. For example, if the normal expected current draw is 10A and the cable size is 25A, then a fuse rated at 15A would be appropriate."


50A fuse would be for 6Ga wire, not for 8ga-26ga wire.

Granted, bare UNinsulated wire can sustain higher current than insulated wire, but, it isn't like one is going to install and use UNinsulated wire for this use.

Where to place the fuse?

Generally, as close to the power source (IE 12V battery in the case of the OPs situation) as possible, I have often seen references of 18" or closer to the battery..

On edit..

I will also add that if you have wire which has more capacity than the expected load, you can use a lower amperage fuse.

In other words, if you had 8 ga wire which would typically be fused at 40A but your device (like a 400W inverter) draws 35A at max full load you could fuse to the max load of the inverter which would be 35A.. But cut that too close and you may get nuisance blown fuses..

The idea of using larger wire sizes than needed is not to handle more current, but to lower the voltage drop seen by the inverter.. Just .1V extra drop in the wire can make the difference between the inverter working or shutting down in 12V systems.

* This post was edited 07/16/22 11:09am by Gdetrailer *

pianotuna

Regina, SK, Canada

Senior Member

Joined: 12/18/2004

View Profile


Offline
Posted: 07/16/22 11:31am Link  |  Quote  |  Print  |  Notify Moderator

freewayrandy wrote:

Thanks for all the info. Pretty lame on electrical here. Inverter primarily for TV. What would be recommended fuse size?


#8 wire with 40 amp fuse (slow blow optional), or a 40 amp breaker. Place the fuse/breaker as close to the battery bank as possible on the positive lead.

We always fuse to the wire size.


Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 07/16/22 12:37pm Link  |  Quote  |  Print  |  Notify Moderator

Gdetrailer wrote:

50A fuse would be for 6Ga wire, not for 8ga-26ga wire.
NEC allows #8 wire on a 50 amp breaker if the distance is short.

With 105C insulation of marine grade wire the #8 is good for 80 amps if not in a bundle.


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

theoldwizard1

SE MI

Senior Member

Joined: 09/07/2010

View Profile


Offline
Posted: 07/16/22 01:57pm Link  |  Quote  |  Print  |  Notify Moderator

time2roll wrote:


With 105C insulation of marine grade wire the #8 is good for 80 amps if not in a bundle.

#10 is adequate if the distance is on!y a few feet. 40A fuse, as close as possible, to the battery.

Marine grade wire is pre-tinned and should never corrode. It is worth the extra cost.

Microlite Mike

NW Washington State

Full Member

Joined: 10/31/2021

View Profile


Offline
Posted: 07/16/22 05:00pm Link  |  Quote  |  Print  |  Notify Moderator

I find charts for wire size to often be confusing and too broad in their recommendations.

For 12 volt circuits (automotive/RV) I prefer this online calculator.


https://www.wirebarn.com/Wire-Calculator-_ep_41.html


Parameters needed for calculations are the maximum amperage of the device you're going to power (which for Inverters needs to take into consideration surge capacitiy),and the length of the wire in BOTH directions as it's a DC Circuit. If using a chassis/frame ground at each end then just use the total length of the wire between battery and device PLUS the wire from battery to frame and device to frame.

This calculator also shows voltage drop for each wire size and the max length at stated amperage to achieve the desired max percentage voltage drop.


"Knowledge is realizing that the street is one-way, wisdom is looking both directions anyway."


~ Albert Einstein

MrWizard

Traveling

Moderator

Joined: 06/27/2004

View Profile


Offline
Posted: 07/26/22 11:02am Link  |  Quote  |  Print  |  Notify Moderator

8ga minimum 6ga would be better, 40a*12v= 480w ,
If the only thing being powered is the TV and cellphone chargers you can use 10ga, but i prefer going larger as you might someday want full max use from it


I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s


afidel

Cleveland

Senior Member

Joined: 12/23/2016

View Profile


Offline
Posted: 07/26/22 12:18pm Link  |  Quote  |  Print  |  Notify Moderator

Personally I'd use an automotive auto-resetting breaker over a fuse. They are much more waterproof, less of a chance that they'll ruin your outing by nuisance trips, and are just much less of a hassle. At small scales the cost difference is immaterial, for $9 you get 4 fuse holders or 2 breakers, compared to all the other costs in the project it's noise.


2019 Dutchman Kodiak 293RLSL
2015 GMC 1500 Sierra 4x4 5.3 3.42 full bed
Equalizer 10k WDH


wa8yxm

Davison Michigan (East of Flint)

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 07/26/22 04:55pm Link  |  Quote  |  Print  |  Notify Moderator

larry cad wrote:

I=P/V

I=AMPS
p=POWER (OR WATTS)
V=VOLTS

I=425/12=35.4 AMPS

10G wire is rated 30amps.

I would go with #8


Add 10 percent for converter loss and overhead So the "rule of thumb" i use is figure AC watts / 10 volts

For that inverter I'd use standard automotive battery cables (4GA) for runs up to around 5-8 feet.. Longer runs bigger wire.. I'd not go shorter.

One Edit.. I said I would.. I also DID. When I had an inverter in that size class.


Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times


eend

Alberta

Senior Member

Joined: 12/23/2004

View Profile


Offline
Posted: 07/30/22 09:24pm Link  |  Quote  |  Print  |  Notify Moderator

I installed a 1000 watt inverter, I wanted to use 8 gauge wire, but that is hard to find and expensive.
But I bought a cheap set of 12’ 8 gauge booster cables for $13.00 at our local Canadian tire store,
Cut the clamps off, and soldered new round connectors on , and works perfectly.


2019 VW Tiguan
2015 F150 ecoboost
2013 Arctic Fox 22G
1971 Boler 1300

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Prev

Open Roads Forum  >  Tech Issues

 > Inverter wire size?
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2023 CWI, Inc. © 2023 Good Sam Enterprises, LLC. All Rights Reserved.