I have a 2003 DS 50amp It is currently plugged in to my 30amp server at my house. Im using 2×25ft 50amp cords.At first it's show 111volt turn on the A/c it drops 108 or so. What could be causing this? But with I run the generator it's fine 115 120. Thank you in advance.
1994 Holiday Rambler Imperial DP
1999 Honda Accord V6 Toad
14 REPLIES 14

BB_TX
Nomad
Nomad
wa8yxm wrote:
He said 10/2

He shoudl be running 8/2 + Ground in the house or even 6/2 if the run is very long... I used smaller wire.. but also lower current.

The OP did not say 10/2. That was a later poster. The OP never came back.

wa8yxm
Explorer III
Explorer III
He said 10/2

He shoudl be running 8/2 + Ground in the house or even 6/2 if the run is very long... I used smaller wire.. but also lower current.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

LouLawrence
Explorer
Explorer
I am curious if you know what size wiring is running to the house 30 amp plug. If it's too small, any load on the line is going to drop the voltage quickly. If you find you do need to upgrade the wiring to that 30 amp plug, consider upgrading the plug to 50 amp with the required larger wiring.

wa8yxm
Explorer III
Explorer III
Bruce Brown wrote:
Voltage drop through the extension cords.


Yup. 111 is just above the "Danger Zone" (less than 110)

And with two cords and two PAIR of plugs and outlets.

Now you might try.
Polishing the plug blades and if you can the parts in the outlets.. Other than the primary (unplug first) you might use a emery board in the outlets to polish. they are right close to the thickness of the blade Just a few in-out-in-out cycles

DE-OX-IT is also a good product. It's followed by a number usually between 5 and 100.. The bigger the number the better the number the nmbers are bigger at Micro Center stores.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

pianotuna
Nomad II
Nomad II
Consider an auto former at the RV end of the cords.

Roll your own extension cord with thicker wire.

Don't exceed 24 amps of demand.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

BB_TX
Nomad
Nomad
If those are true 50 amp extension cords, voltage drop should not be the problem on 30 amp power. Starting with 111 volts and dropping to 108 when you turn on the AC makes me think you have a supply source problem. Especially since it is ok with the generator. Make sure you have 120 vac at the outlet. And make sure the outlet wiring is good and the outlet contacts are not loose, worn, or corroded.

jjj
Explorer
Explorer
I ran my 30 amp plug from my panel to where my trailer
is parked.I used 10/2 wire, had to run it through the
attic. I get 118/119 volts with no load but when ac runs
it drops to about 110 volts.I should have ran 8/2 even 6/2
due to the 50 ft.run and the heat in the attic during the
summer. Your voltage drops seems normal especially with extension
cords.
2002 F-350 Crew-Cab Dually
V-10-4.30 gears Mag-Hytec diff.cover
w/Amsoil-6.0 trans cooler Curt Q5 20K hitch & bedsaver
2005 Keystone Challenger 34TBH-Fifth Airbourn

time2roll
Explorer II
Explorer II
What is the voltage at the house main panel? 111 with minimal load seems low for a grid powered home. May need the electric company to come out and verify. s/b solid 118-122

Possibly the RV water heater is on electric and pulling the voltage down.

valhalla360
Nomad II
Nomad II
What's the voltage if you check at the outlet?

When you apply an electrical load, one of the side effects is it pulls the voltage down. There 3 primary things that impact how much the voltage is pulled down:
- How many amps.
- How long is the electrical cable/wire run (if you coil up 100ft of cable, it still counts as 100ft)
- How thick are the wires
(there are a few other things but not too relevant to this discussion).

The air/con is generally the biggest load in an RV, so relatively high amps. (and as the voltage drops, the amps increase to compensate)
You've had to string together multiple cords, so relatively long cables.
You say it's 30amp service. Is it really 30amp service or is it a 15/20 amp household plug with an adapter. The wiring in your house counts as part of the cabling length and if it's thin, that could be increasing voltage drop.

Dropping by 3 volts is not uncommon with a heavy load like an air/con. If you are starting with a good strong supply up around 120v, that leaves you at 117v which is perfectly fine.

At 108v, that's getting borderline where I would be looking at pulling out the generator. Keep in mind, as houses in your neighborhood turn devices on and off the voltage will fluctuate, so it might be 108v while you are looking and it might drop to 105v a few minutes later.

I'm speculating a bit but if the 111v is while nothing is on in the RV (negligible voltage drop), the voltage at the outlet is likely marginal. Items you can check:
- Are all the connections in good shape with no corrosion? If you are capable, check inside the outlet and at the breaker panel for corrosion or lose wires.
- Check the voltage at other outlets around the house. If they are all down around 110v +-, it's likely nothing wrong with your RV and just that your house has low voltage. You could check with the power company but unlikely they would do anything about it.
Tammy & Mike
Ford F250 V10
2021 Gray Wolf
Gemini Catamaran 34'
Full Time spliting time between boat and RV

larry_cad
Explorer
Explorer
For a nominal voltage of 120V, ANSI allows a range of 104.4 - 127.2 as acceptable. However, NEMA requires electrical equipment be able to operate within a range of 103.5 -126.5. Following either requirement, the OP is able to use his AC within a safe, specified range.

As an aside, the (one way) resistance of 50ft of #8AWG wire is 0.031 OHMS. The round trip resistance total would be .062 OHMS. Assuming a single A/C running at 14Amps, voltage drop is (E=IxR)=14x.062= 0.868V If both A/C units are turned on, total amps would be 28, or 28x.062=1.736V drop. With 111V in at the house, minus 1.736V drop, the voltage at the RV should be about 109V. OP claims 108V or about right.

Still within "code" range of 104.4V or 103.5V for acceptable operation.
Today is my personal best for most consecutive days alive.

Our Travel Blog

wildtoad
Explorer II
Explorer II
I suspect DS is Dutch Star (Newmar). “Server” may be “Service”. Is it possible to move closer? You might want to consider upgrading the service to 50 amps.

As above the length of cords will reduce the voltage. Generator is properly sized for the MH providing 50 amps, and is really really close by.
Tom Wilds
Blythewood, SC
2016 Newmar Baystar Sport 3004
2015 Jeep Wrangler 2dr HT

Bruce_Brown
Moderator
Moderator
^^^ It says he's plugged into a 30 amp at his house.
There are 24 hours in every day - it all depends on how you choose to use them.
Bruce & Jill Brown
2008 Kountry Star Pusher 3910

rk911
Explorer
Explorer
if it drops below 108v i'd disconnect before damage is done. but what's a 'DS' and what is a 30-amp "server"? do you mean a 30-amp outlet at a campsite? but the first response is likely correct...voltage drop through the cords. did you measure the voltage at the post?
Rich
Ham Radio, Sport Pilot, Retired 9-1-1 Call Center Administrator
_________________________________
2016 Itasca Suncruiser 38Q
'46 Willys CJ2A
'23 Jeep Wrangler JL
'10 Jeep Liberty KK

& MaggieThe Wonder Beagle

Bruce_Brown
Moderator
Moderator
Voltage drop through the extension cords.