Wired same as your home and works the same. 240v between the hots and 120v from each hot to neutral.
Generally this is called split phase service. Yes virtually no RVs utilize the available 240v.
12,000 watts of electric power available.


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

AllegroD

Outdare

Senior Member

Joined: 05/13/2003

View Profile



Posted: 01/01/23 01:03pm Link  |  Quote  |  Print  |  Notify Moderator

A link and pic as sometimes the visual helps.

RV 50amp

More reading

[image]

One thing the pic provides is how your RV handles L1 & L2, at the RV distribution panel. You can, therefore, audit what is wired to each leg, such as ACs, inverters/chargers, and 110 plugs, in case you wish to use high load items, such as space heaters.

wa8yxm

Davison Michigan (East of Flint)

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 01/01/23 02:14pm Link  |  Quote  |  Print  |  Notify Moderator

David0725 wrote:

Can someone explain how the 50 approach system works? Normally 50 amp is 220 but the rv is not 220 its 110 riright? So how does this work?


Ok think of your house for a moment.. Most everything in it is 120 VAC but the "Drop" is 3 wires. 240 volt "Divided" as a cook would say (and that is the best term for it.) If you want the technical description Well.. I can do that. Most folks get it wrong by the way.

The divided means you have to "Hot" legs and a "neutral" which is bonded to Ground.. Your devices. Computers. Cloths washer, Fridge, TV/Radio. lights.. Draw off one of the hot legs with respect to neutral. Now some things.. Like a cloths dryer or a Centeral AC use the full 240 volts.. (This is not so in an RV but it is in a house)

So why 240 volts divided?

Imagine that between your electric coffee maker and the power company transformer there are 2 volts of drop. due to the resistance of the wire EACH WAY.. This means you only have not 120 volt but 116 so it takes a but longer before the Elixer of the Gods is ready to drink.

On 30 amp service this is how it works

Now on 50 amp.. let's say that coffee maker is working opposite your Water heater.. IT also has 2 volts drop each way.. but it's on the OTHER LEG. Since the current is nearly balanced the power say comes in Leg 1. losing 2 volts. passes to leg two where it again looses two volts. but now each appliance has not 116 but 118 volts (The voltage drop. like the voltage, is split is.. "Divided")

This means they can use less copper and get better performance.

But due to the neutral wire (the divider) everything gets close to 120 volt.


Think of a water system.. You have two water pups pushign 120 gallons per minute.. both pushign to the right.. in the middle is a "T" and that T is hooked to a tank holding 50 gallons.

So long as both pumps are pumping the fill flow. the 50 gallon tank water level is static.

But what happens if you are only using power on one leg?
Well then the neutral carries that back to the transformer and of course you get voltage drop both ways.

And the level in the tank change in the water example (The rate of change is affected by the size of the pipe by the way.. and the length)

On a good system it takes a very good Digital meter to see the voltage chagnes properly.


Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times


valhalla360

No paticular place.

Senior Member

Joined: 08/19/2009

View Profile



Good Sam RV Club Member


Posted: 01/01/23 06:31pm Link  |  Quote  |  Print  |  Notify Moderator

time2roll wrote:

12,000 watts of electric power available.


Minor nitpick.

You have 2legs @ 6000w.

If you try to pull 8000w on leg 1 and 4000w on leg 2, expect it to pop the breaker.

Of course, that's a lot of power, so unless you are running several space heaters, it's not likely to happen.


Tammy & Mike
Ford F250 V10
2021 Gray Wolf
Gemini Catamaran 34'
Full Time spliting time between boat and RV


ScottG

Bothell Wa.

Senior Member

Joined: 02/25/2005

View Profile



Posted: 01/01/23 08:09pm Link  |  Quote  |  Print  |  Notify Moderator

dougrainer wrote:

RCMAN46 wrote:

The 50 amp 220 volt is the same as the 30 amp 220 volts at your home.
Most RV's loads are 110 volts thus only use one side of the 220 volts as do most of the loads at your home. Most homes only the water heater, electric range and electric furnace use 220 volts and most are 30 amps or less with the exception of some heat pumps. A heat pump in a RV may be wired for 220 volts.


NO HP in a RV is wired for 220 volts. No such HP for an RV has 220 volts. ALL are 110 volts.

220/240 volts in an RV is supplied by 2 separate 120 wires OUT OF PHASE. EACH side is on a 50 amp breaker for 100 amps total supply. The RV does NOT separate the supply. The supply is already separated at the POLE. If the Supply is in phase, the RV will not function correctly all the time. For instance, you have a built in EMS (energy management system) . IT sees if the supply is out of phase. IF IT IS, then you have full 100 amp capacity. IF same phase at supply the EMS will only allow 30 amps total operation. It assumes you have connected a 50 to 30 amp reducer dogbone. IF you think you are connected to a 50 amp service and your EMS shows 30 amp, you have what I call CHEATED 50 amp service. The RV park did not upgrade their supply and wiring for true 50 amp total 100 amp service. This is theft by the RV park. You are paying for 50 amp service and they are NOT giving you what you pay for. The simple test ALL RV'ers need to do is have a multitester and at the Park Pole test the voltage between the 3 and 9 o clock spade slots. 50 amp will show 240. ANY OTHER reading, the pole is NOT 50 amp. Doug


A good explanation. Only thing wrong with it is that the "out of phase" part - a common misconception.
They (the two legs) are in-phase with each other and maybe easier to understand as two halves of the same phase. On an oscilloscope the signal would look like one complete sine wave. That phase is then split into the two, 120VAC legs.
So your 240VAC service is referred to as Split-Phase.

* This post was edited 01/01/23 08:16pm by ScottG *

time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 01/01/23 08:16pm Link  |  Quote  |  Print  |  Notify Moderator

valhalla360 wrote:

time2roll wrote:

12,000 watts of electric power available.


Minor nitpick.

You have 2legs @ 6000w.

If you try to pull 8000w on leg 1 and 4000w on leg 2, expect it to pop the breaker.

Of course, that's a lot of power, so unless you are running several space heaters, it's not likely to happen.
Yes the 12,000 watts would have to be split perfectly half to each side. Still available and would be eight 1500w space heaters if all are on separate branch circuits and four on each side.

I throw out the 12kW power to compare to 30 amp service at just 3.6kW. Big difference.

rgatijnet1

Florida

Senior Member

Joined: 06/22/2009

View Profile



Good Sam RV Club Member


Posted: 01/02/23 04:36am Link  |  Quote  |  Print  |  Notify Moderator

It is also necessary to remember that some inverter/chargers use "pass thru" current when hooked up to shore power. Just because you have x amount of power available from the shore connection does not mean that you can actually use all of it. If I tried to use too many high power appliances it would pop the break on the inverter/charger first. I never tripped a breaker in my main panel or on the shore panel.

pianotuna

Regina, SK, Canada

Senior Member

Joined: 12/18/2004

View Profile


Offline
Posted: 01/02/23 07:25am Link  |  Quote  |  Print  |  Notify Moderator

Best practice is to use not more than 80% of the capacity for continuous loads.

I set my inverter charger to that level (24 amps; 2880 watts) and use the load support feature.

On 50 amps each leg would be set at 40 amps; 4800 watts.

NEC suggests this for sticks and bricks homes. RV's are considered a plug in device and so there is no requirement to follow the 80%.


Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

dougrainer

Carrolton, Texas

Senior Member

Joined: 06/11/2007

View Profile


Offline
Posted: 01/02/23 09:00am Link  |  Quote  |  Print  |  Notify Moderator

ScottG wrote:

dougrainer wrote:

RCMAN46 wrote:

The 50 amp 220 volt is the same as the 30 amp 220 volts at your home.
Most RV's loads are 110 volts thus only use one side of the 220 volts as do most of the loads at your home. Most homes only the water heater, electric range and electric furnace use 220 volts and most are 30 amps or less with the exception of some heat pumps. A heat pump in a RV may be wired for 220 volts.


NO HP in a RV is wired for 220 volts. No such HP for an RV has 220 volts. ALL are 110 volts.

220/240 volts in an RV is supplied by 2 separate 120 wires OUT OF PHASE. EACH side is on a 50 amp breaker for 100 amps total supply. The RV does NOT separate the supply. The supply is already separated at the POLE. If the Supply is in phase, the RV will not function correctly all the time. For instance, you have a built in EMS (energy management system) . IT sees if the supply is out of phase. IF IT IS, then you have full 100 amp capacity. IF same phase at supply the EMS will only allow 30 amps total operation. It assumes you have connected a 50 to 30 amp reducer dogbone. IF you think you are connected to a 50 amp service and your EMS shows 30 amp, you have what I call CHEATED 50 amp service. The RV park did not upgrade their supply and wiring for true 50 amp total 100 amp service. This is theft by the RV park. You are paying for 50 amp service and they are NOT giving you what you pay for. The simple test ALL RV'ers need to do is have a multitester and at the Park Pole test the voltage between the 3 and 9 o clock spade slots. 50 amp will show 240. ANY OTHER reading, the pole is NOT 50 amp. Doug


A good explanation. Only thing wrong with it is that the "out of phase" part - a common misconception.
They (the two legs) are in-phase with each other and maybe easier to understand as two halves of the same phase. On an oscilloscope the signal would look like one complete sine wave. That phase is then split into the two, 120VAC legs.
So your 240VAC service is referred to as Split-Phase.


I think my explanation is better on the Phasing. Please explain in your definition, why, when people try CHEATED 50 amp. They use the same "leg" and then attempt to split that leg onto BOTH sides of the 50 amp RV breaker box, you are still on one phase. This is the Electrical definition of this, NOT MINE. "Two 120 V AC lines are supplied to the premises that are out of phase by 180 degrees with each other". Doug

PS, the definitions also state Split Phase as the same, but I feel stating OUT OF PHASE is better to let lay people understand WHY 50 amp is as it is. It helps explain the 240 between the legs.

rgatijnet1

Florida

Senior Member

Joined: 06/22/2009

View Profile



Good Sam RV Club Member


Posted: 01/02/23 02:34pm Link  |  Quote  |  Print  |  Notify Moderator

https://i0.wp.com/makezine.com/wp-conten......../2016/11/figure_2-240v-1.png?w=450&ssl=1

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 4  
Prev  |  Next

Open Roads Forum  >  Class A Motorhomes  >  All

 > How does 50 amp work?
Search:   Advanced Search

Search only in Class A Motorhomes


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2023 CWI, Inc. © 2023 Good Sam Enterprises, LLC. All Rights Reserved.