Bamshell wrote:
Finally fixed!! After buying a new control board and 2 thermostats it ended up being a $20 temp sensor for the coil which was actually the very first thing i looked at.. i tested both for continuity and neither had it so i ruled it out because 1 unit was working fine. Turns out i needed to ohm it out. The giod one had 11k ohms and the other was 80k ohms.. i swapped them out and then the unit worked.. in hind sight i see why it would let the heat pump come on and not the a/c. 6 hrs of trouble shooting and it was the very first thing i looked at. Oh well hope this helps someone!
Jan-19-2023 01:36 PM
Jan-16-2023 10:17 AM
Jan-16-2023 09:31 AM
Jan-15-2023 11:17 AM
Jan-15-2023 08:35 AM
Bamshell wrote:
Thanks for all of the replies! Im leaning towards it being the tstat and here is why.. zone 2 is the back unit and if i switch to heat pump neither the compressor or the fan comes on. I am plugged into 50 amp ac now btw. If i go to cool, the fan comes on, no compressor. Also i just fired up my LP furnace and zone 1 seems to work perfect. When i try zone 2 on the gas heat it does nothing. I can tell there must be a separate fan for the rear zone because i have vents down low with no air flow coming out.. any feedback is greatly appreciated