Good Sam Club Open Roads Forum: Atwood lp Stove Flame starts to die
Open Roads Forum Already a member? Login here.   If not, Register Today!  |  Help

Newest  |  Active  |  Popular  |  RVing FAQ Forum Rules  |  Forum Posting Help and Support  |  Contact  

Search:   Advanced Search

Search only in Tech Issues

Open Roads Forum  >  Tech Issues

 > Atwood lp Stove Flame starts to die

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Prev
JBarca

Radnor, Ohio, USA

Senior Member

Joined: 12/16/2004

View Profile





Offline
Posted: 04/06/23 06:20pm Link  |  Quote  |  Print  |  Notify Moderator

pmlevine wrote:

To continue this thread regarding the diminishing flame on a lp stove Dometic/Atwood model RV-1735 BBP (flame starts high and blue, diminishes to a yellow flame after 5 minutes)...
The refrigerator and furnace work fine, I believe the stove issue is part 51062, the stove regulator ($50 item). Part replacement seems problematic: out of stock or has quality control issues.
I brought my RV in for service today, providing the above info.
If a $50 replacement part is not an option, what options might I have? Replace the top assembly of the stove for $$$ ?
I will report back on this thread after hearing from the RV service center, hoping a part replacement resolves the issue.


If the shop finds the stove regulator to be the issue, I would hope they can find an alternate regulator. These are not really special stove regulators, but they do need to fit in the space provided and regulate correctly. Having to buy a completely new stove top just to get a stove regulator is, well, not right.

Yes, please let us know how this comes out.

John


John & Cindy

2005 Ford F350 Super Duty, 4x4; 6.8L V10 with 4.10
CC, SB, Lariat & FX4 package
21,000 GCWR, 11,000 GVWR
Ford Tow Command
1,700# Reese HP hitch & HP Dual Cam
2 1/2" Towbeast Receiver

2004 Sunline Solaris T310SR
(I wish we were camping!)


dougrainer

Carrolton, Texas

Senior Member

Joined: 06/11/2007

View Profile


Offline
Posted: 04/07/23 10:07am Link  |  Quote  |  Print  |  Notify Moderator

JBarca wrote:

pmlevine wrote:

To continue this thread regarding the diminishing flame on a lp stove Dometic/Atwood model RV-1735 BBP (flame starts high and blue, diminishes to a yellow flame after 5 minutes)...
The refrigerator and furnace work fine, I believe the stove issue is part 51062, the stove regulator ($50 item). Part replacement seems problematic: out of stock or has quality control issues.
I brought my RV in for service today, providing the above info.
If a $50 replacement part is not an option, what options might I have? Replace the top assembly of the stove for $$$ ?
I will report back on this thread after hearing from the RV service center, hoping a part replacement resolves the issue.


If the shop finds the stove regulator to be the issue, I would hope they can find an alternate regulator. These are not really special stove regulators, but they do need to fit in the space provided and regulate correctly. Having to buy a completely new stove top just to get a stove regulator is, well, not right.

Yes, please let us know how this comes out.

John


John, wrong! The Stove/range LP regulator IS a special regulator. The stove/ranges run of 10 inches W/C, NOT 11.5 WC. The Stove regulator drops the 11.5 down to 10 inchs W/C. So, you need the regulator built for 10 inches W/C. It is rare for this regulator to fail for pressure. Usually leaks. The OP needs to connect a seperate 20lb LP tank with the hose and 3/8 connector DIRECT to the stove and then test run. I believe his problem is the rubber LP supply line is slightly kinked causing it to run for a few minutes, and then goes out. This is especially true if the Stove is mounted in a slide room. Doug

JBarca

Radnor, Ohio, USA

Senior Member

Joined: 12/16/2004

View Profile





Offline
Posted: 04/07/23 10:54am Link  |  Quote  |  Print  |  Notify Moderator

dougrainer wrote:

JBarca wrote:

pmlevine wrote:

To continue this thread regarding the diminishing flame on a lp stove Dometic/Atwood model RV-1735 BBP (flame starts high and blue, diminishes to a yellow flame after 5 minutes)...
The refrigerator and furnace work fine, I believe the stove issue is part 51062, the stove regulator ($50 item). Part replacement seems problematic: out of stock or has quality control issues.
I brought my RV in for service today, providing the above info.
If a $50 replacement part is not an option, what options might I have? Replace the top assembly of the stove for $$$ ?
I will report back on this thread after hearing from the RV service center, hoping a part replacement resolves the issue.


If the shop finds the stove regulator to be the issue, I would hope they can find an alternate regulator. These are not really special stove regulators, but they do need to fit in the space provided and regulate correctly. Having to buy a completely new stove top just to get a stove regulator is, well, not right.

Yes, please let us know how this comes out.

John


John, wrong! The Stove/range LP regulator IS a special regulator. The stove/ranges run of 10 inches W/C, NOT 11.5 WC. The Stove regulator drops the 11.5 down to 10 inchs W/C. So, you need the regulator built for 10 inches W/C. It is rare for this regulator to fail for pressure. Usually leaks. The OP needs to connect a seperate 20lb LP tank with the hose and 3/8 connector DIRECT to the stove and then test run. I believe his problem is the rubber LP supply line is slightly kinked causing it to run for a few minutes, and then goes out. This is especially true if the Stove is mounted in a slide room. Doug


Hi Doug,

I can tell by your response you may have taken my set of words out of context. I fully agree with what you are saying about the function of a "stove regulator". The term used in industry as a step-down regulator on a range.

I used the wording "stove regulator" as a specific device. Not a main tank (2-stage) regulator. I'm sure you will agree on the purpose of a "stove regulator" in a camper serves the same purpose as a stove regulator in a home stove/range. The purpose is to drop the stove supply pressure down to 10" WC to allow the stove to burn more consistently when other appliances on the 11" WC LP line starts and stops as the main tank regulator adjusts for LP loads on the main line. In the camper, when the furnace kicks on, the main line may boost up 12 or 13" WC and come back down closer to the 11" WC setpoint. The "stove regulator" tames this spike down to a more even 10" WC if it works correctly. Agree?

My point was, if the shop states they have to sell an entire range top to get a new stove regulator, that's not right. You got to be kidding me if they do say that. If Dometic is having a supply issue, an alternate, correctly sized, stove regulator can be used.

Atwood went through several different brands of stove regulators over the years, I'm sure you saw that. And so has Suburban.

Your kinked rubber hose thought, yes, good thought, I did not think of that, it is possible., Good point.

John

groundhogy

PA

Senior Member

Joined: 12/17/2014

View Profile


Offline
Posted: 04/08/23 08:27pm Link  |  Quote  |  Print  |  Notify Moderator

What about other appliances that use propane, are they experiencing difficulty?
Hot water heater
Furnace

pmlevine

Massachusetts

New Member

Joined: 07/05/2016

View Profile


Offline
Posted: 04/15/23 01:11pm Link  |  Quote  |  Print  |  Notify Moderator

OP here. I picked up our TT from service, they could not find any issues with the lp stove, they informed me the stove passed a leak test. The also told me they could not duplicate the stove going to a low yellow flame, but I doubt they let the stove run long enough to see that. The furnace and frig don't have any issues running from lp.
I changed out the lp alarm last month since the original one just exceeded the expiration date.
So we are looking forward to starting our RV trips, locally here in New England.
Thanks to all for the advice.
Phil


C Schomer

Pueblo West, Co.

Senior Member

Joined: 12/26/2000

View Profile


Offline
Posted: 04/15/23 05:29pm Link  |  Quote  |  Print  |  Notify Moderator

I’ve used plenty of adjustable, regulators and set them to the pressure required. There are some really tiny regulators, even meant for pilot lights. You can usually find a manufacturers BTU rating on regulators
There is also a little bit of oil in propane from the industrial pumping equipment, and it can precipitate out into the end users systems. I’ve had to take sensitive equipment apart and clean out that oil.
I have several water column gauges but I used Fluke bench equipment to check the calibration and I’ve had to write a correction chart on each one of them. So just use a water column because that is the gold standard… W.C.
Always make sure you have a quick way to turn off the gas when working on gas appliances, accidents can happen! Craig

pmlevine

Massachusetts

New Member

Joined: 07/05/2016

View Profile


Offline
Posted: 04/15/23 06:20pm Link  |  Quote  |  Print  |  Notify Moderator

C Schomer wrote:

I’ve used plenty of adjustable, regulators and set them to the pressure required. There are some really tiny regulators, even meant for pilot lights. You can usually find a manufacturers BTU rating on regulators
There is also a little bit of oil in propane from the industrial pumping equipment, and it can precipitate out into the end users systems. I’ve had to take sensitive equipment apart and clean out that oil.
I have several water column gauges but I used Fluke bench equipment to check the calibration and I’ve had to write a correction chart on each one of them. So just use a water column because that is the gold standard… W.C.
Always make sure you have a quick way to turn off the gas when working on gas appliances, accidents can happen! Craig


Thanks Craig. The possible particulate residue from oil in the propane raises an interesting question. What is the wisdom of placing a high flow disposable filter in-line before the appliances to avoid particulates from impacting the function of stoves, furnaces, water heaters, refrigerators ?

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Prev

Open Roads Forum  >  Tech Issues

 > Atwood lp Stove Flame starts to die
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2023 CWI, Inc. © 2023 Good Sam Enterprises, LLC. All Rights Reserved.