Suburban SW10PE - pilot works, but main burner won't light

truthsmiles
Explorer
Explorer
Hi all - first time poster. Just bought a very neglected RV (brand unknown - even DMV couldn't figure it out from the VIN - but that's a question for another day!)

As the title implies, my RV has the SW10PE water heater - it's the kind with a manual pilot light (no electric ignitor) and a separate AC electric element.

The gas valve is a SIT-610-AC3. Here are some images stolen from amazon - pictured is exactly what I have...

Front:


Back (you can see the thermostat probe here):


The symptoms are that I'm able to light the pilot and turn the valve to "ON", and the pilot stays lit. So, I know the thermocouple is working and the gas valve is at least partially functional.

However, no matter where I set the temperature the main jet doesn't light. I've yet to disassemble and clean it (I know spiders like those tiny holes), but the soap bubble test shows nothing at all coming out.

So, at this point I suspect it may be the thermostat that's faulty. To be sure, the condition of the tank may be REALLY bad. The sacrificial anode is completely gone and the electric element is open, so it wouldn't shock me if the gas valve thermostat is corroded/shot.

Related, I found ***Link Removed*** where the user describes a gas valve that won't shut off (overheats the tank) and the consensus seemed to be a faulty thermostat. Mine is the opposite problem, of course, but before I go making assumptions I thought I'd ask the experts here!

So, here are my questions:

1) Is there a test I can perform to confirm a faulty thermostat? Is there an ohm specification? Or should it just be 'closed' (0 ohms) when heat is needed? Is there any other recommended testing procedure?
2) If I can confirm the thermostat is faulty, does anyone have a link to a replacement part? I'd hate to replace the entire gas valve if that's the only problem.

Thanks!
7 REPLIES 7

truthsmiles
Explorer
Explorer
UPDATE: Just wanted to circle back here for anyone else happening upon this post.

Counter to the advice I was given, I ended up taking the gas valve apart, applying my best troubleshooting skills, and then when I didn't find anything obvious, re-assembling it.

I installed it back on the RV and shortly after I lit the pilot light flames sprang forth from all around the valve! Fortunately I was watching and forcefully blew on the flames, which put them out for a second and I was able to shut off the valve. So, obviously I didn't put it back together correctly ๐Ÿ˜•

So, lesson learned, and @Old-Biscuit was 100% right. I shouldn't have messed with the gas valve and just replaced it - which I did, and it worked perfectly ๐Ÿ™‚

PS - As it turns out the reason the old valve wasn't working was that it was filling with water. The plastic cover on the temperature probe had been compromised by the threads on the tank and water was leaking in. Photo attached.

truthsmiles
Explorer
Explorer
Old-Biscuit wrote:
Gas valves are NOT SERVICEABLE

Thermistor???
That is a temp sensor for a fridge

What are you referring?
Thermocouple? (Pilot flame is staying ON so thermocouple IS working---it generates millivolts that HOLD magnet open allowing gas flow. When you push down on knob you are bypassing that to get gas flow....then thermocouple takes over)

And that probe out the backside...
That is the ECO (Energy Cut Off....a high temp probe. BLOWS if water temp gets to 190*F to shut down ALL gas flow--no pilot/no main. Gas Valve has to be replaced if it blows)


Thanks for the additional reply!

No, I'm not referring to the thermocouple - the pilot light stays lit so clearly that part of the gas valve is working (there is voltage from the thermocouple, and that voltage is holding the solenoid open).

And, yes I agree the ECO inside the probe is intact or there would be no gas flow at all (even to the pilot).

What I was referring to was the 'main' side of the valve... obviously the gas valve must sense the temperature of the water somehow (via the probe, I assume), and that in turn controls whether the main valve is open. As far as I know, the thermostat must be purely mechanical (bi-metallic?), or it's electrical and there's a thermistor that allows/disallows current to flow through a second solenoid to open the main valve. By your reaction it sounds like it's the former - so thanks!

I do understand that the standard answer is to say "It's not serviceable - you have to replace it!", but I was hoping a DIYer who has opened one up and fixed it might be able to tell me whether it's even worth trying.

In any case, I've got some torx security screws on order and plan to crack it open. I'll report back if I'm able to figure it out and fix it! ๐Ÿ™‚

Kind regards.

Old-Biscuit
Explorer II
Explorer II
Gas valves are NOT SERVICEABLE

Thermistor???
That is a temp sensor for a fridge

What are you referring?
Thermocouple? (Pilot flame is staying ON so thermocouple IS working---it generates millivolts that HOLD magnet open allowing gas flow. When you push down on knob you are bypassing that to get gas flow....then thermocouple takes over)

And that probe out the backside...
That is the ECO (Energy Cut Off....a high temp probe. BLOWS if water temp gets to 190*F to shut down ALL gas flow--no pilot/no main. Gas Valve has to be replaced if it blows)
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

truthsmiles
Explorer
Explorer
Old-Biscuit wrote:
Gas tube/orifice blocked....remove/soak in alcohol--blow with LOW pressure air (High Pressure Air or poking things thru orifice will cause damage---it is a metered hole)

Gas control defective---replace gas valve


Thanks for the reply!

I've already removed and inspected the gas tube and orifice - both were clear, I could easily see through and easily pass 'breath' through. There were cobwebs in the burner tube, but gas wasn't even making it out of the orifice.

Is there any hope for servicing the gas valve? I'm still suspecting the thermistor. I know it's not 'normal' to replace it, but I'm down to give it a shot if it'll save me $150. ๐Ÿ™‚

Old-Biscuit
Explorer II
Explorer II
Gas tube/orifice blocked....remove/soak in alcohol--blow with LOW pressure air (High Pressure Air or poking things thru orifice will cause damage---it is a metered hole)

Gas control defective---replace gas valve
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

truthsmiles
Explorer
Explorer
Thanks for the response!
I just tried moving the temp adjustment and it SEEMS to move the shaft, but as you can see in the picture it's completely covered by the plastic cap - so I can't tell if it's actually moving. That being said, it feels exactly how I would expect it to feel: smooth, light resistance. It doesn't 'catch' or 'slip' or feel loose at all.

In any case, it's currently below 30ยฐF outside right now so I'd expect it to come on no matter where it's set(?)

Chris_Bryant
Explorer
Explorer
Thatโ€™s basically a mechanical valve- if the pilot stays lit in the โ€œonโ€ position, the electrical safety fuse is fine, it interrupts the thermocouple current which holds the safety open..
Are you sure the shaft is actually turning when you move the temp adjustment? Iโ€™ve had them freeze up so moving the adjustment doesnโ€™t move anything.