How well does a dual-pigtail like this Camco item work for 15A plus 30A giving you a nominal 45A when they don't have 50A? Reviews at amazon etc are pretty good.
|
wildtoad

Blythewood, SC

Senior Member

Joined: 06/05/2011

View Profile


Good Sam RV Club Member
|
Just a note in that some CG’s don’t allow a site to use more than one socket at a time. Rare, but there are some.
Tom Wilds
Blythewood, SC
2016 Newmar Baystar Sport 3004
2015 Jeep Wrangler 2dr HT
|
larry cad

ohio

Senior Member

Joined: 05/23/2004

View Profile


Offline
|
They work fine if all you need is 15 (or 20) amps from one side, and 30 amps from the other side. Remember, a 50 amp service is actually 100 amps, 50 amps on each of two legs.
Today is my personal best for most consecutive days alive.
Our Travel Blog
|
Chris Bryant

Arden, North Carolina

Senior Member

Joined: 03/26/2003

View Profile

|
They are near worthless, as they will not work if the 15 amp outlet is GFI protected, which they all are required to be.
-- Chris Bryant
|
jdc1

Rescue, Ca

Senior Member

Joined: 05/30/2011

View Profile

Offline
|
One question, three different answers. That's why this forum is so popular. Everyone gets their say, and they don't get ridiculed for it.
|
|
BB_TX

McKinney, Texas

Senior Member

Joined: 04/04/2005

View Profile

Offline
|
Chris Bryant wrote: They are near worthless, as they will not work if the 15 amp outlet is GFI protected, which they all are required to be.
This answer is correct. Newer codes require GFCI outlets. And this device will not work with a GFCI since the common neutral almost guarantees the currents thru the two separate hot outlets will not balance with the neutrals back thru the respective outlet neutrals.
Might work in an older campground that has not been upgraded to GFCI.
|
gbopp

The Keystone State

Senior Member

Joined: 08/03/2008

View Profile

Offline
|
I've never seen this type adapter. If only one male end was plugged in wouldn't the other one be hot?
|
DownTheAvenue

Sunny South

Senior Member

Joined: 07/30/2014

View Profile

|
BB_TX wrote: Chris Bryant wrote: They are near worthless, as they will not work if the 15 amp outlet is GFI protected, which they all are required to be.
This answer is correct. Newer codes require GFCI outlets. And this device will not work with a GFCI since the common neutral almost guarantees the currents thru the two separate hot outlets will not balance with the neutrals back thru the respective outlet neutrals.
Might work in an older campground that has not been upgraded to GFCI.
YUP! This is correct!
|
D.E.Bishop

Eagle Rock, CA

Senior Member

Joined: 08/09/2001

View Profile


Good Sam RV Club Member
Offline
|
jdc1 wrote: One question, three different answers. That's why this forum is so popular. Everyone gets their say, and they don't get ridiculed for it.
Read the first two pages of the post "Long Arm of the Law".
This is my first post in a long, long time and probably my last for even longer. Gary's post was a good one, answers 18 thru to the end are in left field and off topic.
"I travel not to go anywhere, but to go. I travel for travel's sake. The great affair is to go". R. L. Stevenson
David Bishop
2002 Winnebago Adventurer 32V
Back to a 2006 Suzi GV
Roadmaster 5000
Roadmaster Invisibrake
|
enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile


|
Older campgrounds have the 15 amp and 30 amp on the same leg of power source. The unit in question normally have a disclaimer about this.
50 amp rigs are specified the feed to be 120/240 four wire.