enblethen wrote:
colors appear to be correct with provided model number.
How does the stove top flames look? Turn on all and see if flame turns yellow. This is sign of bad regulator.
Check electrode for proper spacing.
Remove cover from the thermostat. check how many wires. If only two wires connect them together. Furnace should cycle on and provide heat with no shut down. Separate the two wires, furnace should go into cool down mode and shut down.
โOct-19-2020 09:13 AM
โOct-19-2020 08:19 AM
Bud
USAF Retired
Pace Arrow
โOct-19-2020 08:11 AM
wa8yxm wrote:
Ok Starts. then shuts off (3 times) then locks out Each time it lights but then shuts off.. Sounds very very very familure (As in I had that problem).
Suspect list:
An obstruction in the burner orifice (Gas jet) or elsewhere can cause a weak flame. I do not think this is it
A deffective thermocouple may not detect the flame. I've heard of this but again I do not think it is common.. If it's all cruded up with carbon it might be and issue.
Bad connection between Thermocouple and mother board (NOTE on a single wire system the wire is the ignition wire) this can do it. After all ignition is like 1000 volts AC and Sense is 1/2 volt DC so the kilovolt will overcome a bad connection and actually make it worse.. However again I think rare.> Still easy to check (just pull and reconnect the connectors a few times each one on each end of the wire)
Bad control board (Motherboard) DING I found my winner..
THeory (And support to follow) is that if the swichover from SEND SPARKS to Look for .480 volts from thermocouple goes flakey then the sensor chip gets hit with up to 1500 volts and POP goes the wafer. So no heat sense.
Solution was a new board from DINOSAUR boards.
Support for my theory: ON the Dino broad right about where I suspect that sensor chip is there is a nifty gas discharge tube. This tube is a "Surge Suppressor" type device (like the MOV in a power strip) that clips and limits the voltage to something the sensor chip can withstand.
My Guess is that Dinosaur Boards and I think alike on this issue.
Other comments: I am a trained Certified Electronics technician who has designed and built some of his own hardware. My initial impression when I took the Dino board out of the box was QUALITY!!!.. and nothing since has changed that impression .. Oh that was 2012 (Feburary) when I opened that box. it still works.
โOct-19-2020 05:47 AM
Bud
USAF Retired
Pace Arrow
โOct-19-2020 05:00 AM
enblethen wrote:
Check the alignment of the flame senor to insure it is directly in the flame.
Black should be ground
red goes to gas valve
white to limit switch
blue connects to the blue from limit switch that ties to the thermostat.
This is according to furnace manual I have.
Exact model of your furnace would help!
โOct-19-2020 04:59 AM
โOct-18-2020 09:38 PM
โOct-18-2020 06:07 PM
Bud
USAF Retired
Pace Arrow
โOct-18-2020 05:59 PM
BFL13 wrote:
Model/year of the furnace? Some have separate heat sensor probes going to the circuit board, while the newer way just has the sparker, but it "reads" the flame magically, so your post is not clear on that. You changed the CB and it did not fix it, so is it the old way you can change the probe that lies alongside the sparker?
That flame sensor probe ( if fitted) has its own wire that can be checked for connection too.