BFL13 wrote:
PD 9280 Specs:
Input: 105-130 VAC, 1,300 Watts
Note: Requires 20 amp rated outlet
Output: 13.6 VDC, 80 Amps
Also see specs table at bottom of this:
http://www.bestconverter.com/9200-Series-Deck-Mount_c_84.html
So what does that all really mean? 13.6 x 80 = 1088w. They claim at least 80% efficiency. 1088/1300 = 83.6% so they are doing the specs at 13.6, not 14.4
At 14.4v, 14.4 x 80 = 1152w output, and at 83.6% efficiency, input would be 1378w
BUT as discovered in the other thread, the PF correction is 0.7 and you use that for input. 1152 x 100/70 = 1645VA drawn from the AC power source.
1645VA requires 12 wire and 20a CB by NEC rules for appliance left on more than 3 hours.
http://forums.trailerlife.com/index.cfm/fuseaction/thread/tid/29016351/srt/pa/pging/1/page/1.cfm
โSep-05-2016 08:29 AM
โSep-05-2016 08:08 AM
โSep-05-2016 07:45 AM
wa8yxm wrote:
The 9280 Plug In model comes with a 20 amp plug, not a more common 15, however it will work just fine on a 15 amp breaker,, you just need to hang a 20 amp outlet in the bay for it to plug into
The hard wired version is even easier.. no need to hang the outlet.
HOW DO I KNOW THIS
I have a 9180 with optional charge wizard.. (Basically the 9280) and I needed the 20 amp breaker for something lese so I hung it on a 15 as I did not have another 20 handy.. Works great, has for 11 years.
โSep-05-2016 07:37 AM
BobKrogstie wrote:
I am looking at a Progressive Dynamics Series 9200 replacement for my now defunct WF-9875 converter but PD does not have a 75A unit. Their 80A unit requires a 20A AC source but my current converter circuit in the basement has a 15A breaker so I'm ruling out the PD 80A unit. This leaves me with the PD9270 as a replacement unit. Would like input as to whether or not the PD9270 is adequate to replace the WF-9875.
โSep-05-2016 06:46 AM
MEXICOWANDERER wrote:
Do any rigs get wired with 12 AWG? All I've seen had 14 AWG.
โSep-05-2016 06:46 AM
MEXICOWANDERER wrote:Our toy hauler has yellow, 12/2, romex run to both air conditioners, the microwave, and to the converter. Each of these four circuits are connected to a 20 amp breaker (total 4).
Do any rigs get wired with 12 AWG? All I've seen had 14 AWG.
โSep-05-2016 06:30 AM
โSep-05-2016 06:12 AM
โSep-05-2016 06:01 AM
bpounds wrote:rhagfo wrote:
:h
Change the breaker to 20 amp, and the outlet to a 20 amp configuration, maybe $15 worth of the parts.
Not knowing the size of the wiring in the trailer, I would never recommend changing the breaker.
Change the outlet, okay. Change the plug on the cord, okay. Because it is still protected by the original breaker.
Moot point though, since the PO has already made a wise decision.
โSep-04-2016 03:14 PM
rhagfo wrote:If the existing wiring will support that amperage (run length and gauge) could be a viable option. However, without knowing the OP's run length and gauge I wouldn't feel comfortable recommending this.otrfun wrote::hBobKrogstie wrote:The WF-9875 in our toy hauler was connected to a dedicated 20 amp breaker, which I believe is what WFCO recommends for the WF-9875. Unless you want to use a 15 amp breaker with the PD9280 (against PD's recommendation), I'd say you have no choice but to go with the PD9270 (or smaller).bpounds wrote:
I think you would be okay either way.
But, where did you get the 20A info? Because I see a draw of 1300W on the input, which would only be 11.x amps. No where near needing a 20A breaker.
Link to a good source:
PD 9280
Here under Specifications: Link to Specs
According to the WFCO WF-9875 installation manual the WF-9875 draws 15.7 amps under maximum load. Slightly more than 15 amps.
Change the breaker to 20 amp, and the outlet to a 20 amp configuration, maybe $15 worth of the parts.
โSep-04-2016 03:00 PM
bpounds wrote:rhagfo wrote:
:h
Change the breaker to 20 amp, and the outlet to a 20 amp configuration, maybe $15 worth of the parts.
Not knowing the size of the wiring in the trailer, I would never recommend changing the breaker.
Change the outlet, okay. Change the plug on the cord, okay. Because it is still protected by the original breaker.
Moot point though, since the PO has already made a wise decision.